Hi,
Recently installed a system with 2 SMA inverters. I've connected the piggyback to one of the inverters and switched the rotary switch to the '1' setting. I have sunny explorer on my laptop but when I search for the piggyback it says no devices found. I've also tried it with the rotary...
Im in the royal engineers and currently in Afghanistan, I've just been tasked to carry out a test and inspection and do not have an on site guide or GN3, and I completed my 2391 2 years ago and not touched it since. Can anyone help me with electronic copies of on site guide or GN3 so i can...
stan@59
Thread
cheers
copies
electronic
guide
testing
though
trouble
recently changed an old fuseboard to a new MK consumer unit with 2rcbo's and then RCD with 5 mcb's on it, now i IR all the circuits and all came out at <299Mohm but since day 1 the rcd has tripped whenever a high load is switched on? i tried the up and down ring and the fridge radial on 1 of the...
jenions
Thread
aus
before
button
circuits
connected
installed
led
newly
removing
trouble
Hello. I have received a request to put a shaver socket in a bathroom, bang in the middle of a porcelain tile. Does anyone have any experience on the best tool, method to use? I have cut plenty of holes in normal tiles for socket outlets using a dremmel quite easily but it doesn't touch the...
New to forum so first post. Hello!
Just installed a 21 x 190Wp system using a SMA SB4000TL inverter. Have 2 strings of 8 on input A and one of 5 on input B.
Keep getting error message 1 stating Too much generation for the inverter and trips out. Will operate on the 5 string but obviously at...
Just had a four hour mcs audit for my renewal, all went well, except for a couple of non conforms, and a strong word of advice, anyone not doing wind cals and structural calcs are going to be in trouble, and they can make you go over all your installs and carry out calculations. I was ok on...
When it comes to 3 cables in one terminal, for example the earth wire, I find it really hard. I'm at college at the moment, with my practical exam, I have gone overtime because of this. I have two cables in then I put the last one in, then screw it in but there is usually one that falls out...
Any help would be appreciated.
Recently had a new boiler with megaflow tank fitted & i've wired up the heating controls according to the s plan diagram inthe booklet for the tank, except for a room stat as i intend to use the thermostatic valves on the rads to control the heat. The problem i'm...
arigurrin
Thread
boiler
heating
problem
programmer
system
trouble
wiring
Just stated out and having installed a few CU's with success i went to a flat today and couldn't find the main fuse. Hoping to find it with the meter it wasn't there. This was next to the old fuse box under a panel. Any ideas??? No doubt you will but many of the old installs baffle me!
Thanks
Danielwareham
Thread
aus
finding
flats
fuse
main
main fuse
phase
probably
supply
trouble
HI All
Ive just finshed installing a small lighting circuit in a toilet riser
The cct is protected by a B 6A MCB and is wired in FP200 2.5MM
I got the following readings Ze was taken at the Db at 0.11 ohm
All insulation resistance readings were taken at 2M ohm
and my R1+R2 was 0.03ohm...
Hello everybody,
This is my first post names Micky. I was wondering if anyone could help me out with this question I’ve have been struggling with it for a long time. As a result I’ve lost a large part of my hair, mainly from the frontal region .
Question: - Given that the resistance per meter...
Hi guys,
Havnig a small drama here at work trying to re-wire a contactor for a three phase motor. The chap that installed the contactor was firstly NOT an electrician, he was in fact a metal worker....and the job he did certainly worked, but was a little unusual to say the least...
i fitted 4 5'twin corrosion proof T8 with electronic ballast
3 of them are giving trouble -sometimes they start
other times not -or might go off after a few minutes
i assume there's a fault with ballast-i doubt it's voltage but will check
anyone had similar issues thanks
Hi,
Apologies if I've put this question in the wrong place (its my first post).
I've just bought a Megger PAT 450 along with the Megger Powersuite Pro-Lite software and am having trouble downloading results. The tester instructions are that results must be taken from the machine with a USB pen...
I have just blown the dust of my Megger MFT1553 and decided to run through some tests as I have a consumer unit to replace tomorrow. First one since passing my Elecsa registration :).
Anyway, I have tried to do a Ze test and I can't get a reading. I am sure I am following the same procedure...
Gerry24
Thread
aus
help
isolator
megger
reading
suppliers
switch
trouble
Right been on a job today to swap an electric oven, done. but while i was there they said they had some lighting problems.
Last night the fuse got blown to bits when they turned the bathroom light off. (yes its an old re wire able fuse box) so i checked in the ceiling rose and everything...
Helo I'm fairly new to this testing so perhaps someone could explain this
My Fluke is giving off some quite varied readings. We we're doing some R1+R2 testing and when I tried to zero the leads it appeared to make no difference and then the circuit reading seemed to be going all over the...
Hi ALL
Have to install a Condenser unit on a roof in the nxt couple of weeks the length of run is around 50M the unit FLC is 24A will be Reference method E on Try for most of the run 4mm swa can take 41A table 4D4A and 6mm can take 53A. Just need some advice regarding VoltDrop
As this is...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc