Hi
I have just rewired a mate’s house with his help and the existing earthling is TT on overheads. We have tried to get it changed to PME (TNC-S) but who do you contact now a days. Back when I did nothing but house bashing in was a piece of cake, now its been split up they keep sending bods...
Would appreciate some advice please.
I'm wiring a TT system and am un-sure of what earthing is required.
Reg 411.3 - 'Requiremnts for fault protection', says that protective equipotential bonding is required to extraneous-conductive-parts which i'd already done. Am i correct in saying that there...
HI, I've been asked to do a pir on a domestic installation, Means of earthing is a TT system using a 100 mA (not s-type) rcd as the main switch, covering all circuits. House is a rental property...Is there any real problem with this with regard to regs? would appreciate any advice thanks.
I am finding this quite a complicated subject, and I would really welcome your thoughts on this subject.
If I could start with a TT system, according to regs, 411.5.3 states that when using an RCD for fault protection purposes, then the following has to be applied.
RaxIn<=50
This means that...
Hi, can anybody throw some light on a problem / confusion i have?
I'm in the process of installing a new TT system.
The existing earth electrode had a high resistance in excess of 2Mohms. I've inserted a new electrode in a new location and measured the resistance immediately after inserting the...
Good Morning
I would like some advice.
Working on a Domestic TT System. Primarily a kitchen refurb. The customer in my case is the contractor. I told him there should be an earth electrode around. I tried to locate and could only locate 6mm earth cable to a disused lead water pipe...
Hi guys, I've got a TT system with a Ze of 21 ohms. Two ring final circuits are on the same rcd and are both giving a Zs of 1.7 ohms - does this indicate a neutral - earth fault?
I am quite interested to know how people would go about this installation.
Install a 3-phase supply from a house to the middle of a field and install a distribution board with main switch. approx 150 mtrs
Then from one phase run away to various outlets for caravans the furthest being 300 mtrs...
Hi all,
Quick question, can you use a 25mm cable from earth bar in C/U to Earth Rod in cellar directly below?
Reason I ask is I need the 3m tails to extend from incoming fuse, and they come with a 25mm earth cable included, so would this be easier than running a new 10mm earth cable to the...
Could the MET for a TT system be an earth bar in a garage CU?
This would then feed the house CU (opposite side of attached garage wall) earth bar using 4mm conductor. All loads are 30ma RCD protected.
Thanks
can anybody help me, a mate of mine has a tt system at home and asked me to test his house as he wants to rent the property. i would just like to no what size earth should it be for a tt system, at the moment its 6mm and without diging me books out am not sure if it requires upgrading and knew...
hi all i ahve been reading up on tt systems am i correct in saying that a tt system can have a lower earthing conductor than a tncs or tns? can anyone explain why? and also what is the lowest earthing size u have seen on a tt system ?
Hi
Recently come across a submain installed in a property that had a 63 amp d type mcb and a 100ma s type rcd as its overcurrant and earth protection. Fair enough. I measured a psc of 558 amps. Voltage 248 amps Ze 128 ohms. At origin. As an mcb is designed to operate in .1 of a second would...
Help!
Sorry having a bad day.
I understand the concept behind touch contact of 50v and the above 1666 ohms. But when physically testing with 17th ed dilog and testing a TT system 30mA RCD. At 1x and 5X what reading would you see on your meter? or would you just test the mechanical aspect...
guys,
been to a house this after noon which is on a tt system. Found that the man rcd before the board has a rated tripping current of 500ma was wondering if this is correct as cannot find it in the regs also is it right that you can only do a half reading and a x 1 reading on this unit.(rcd...
I am wiring an outbuilding, to be used as an office at the moment. I am nearly at the stage of running the supply out to it from the main house.
The main house has a TT supply. Would the correct way to do it be to use a 63a 100ma time delayed rcd to protect the swa supply, and 30ma protection...
Hi guys new to testing and about to do my first TT system tomorrow. Popped in today and did a quick Ze test and got 16.98 ohms. Zs values will not meet max values for 7671. Whats your thoughts guys. (what have I forgotten?). Pete
some asked me about why earthing a garage has to be a tt, ill be honest, i new it had to be done but i couldnt remember why, i knew it had something to do with neutral current but someone enlighten me please