Could you please help me with a couple of queries regarding regulations on a mobile home park?
Firstly, what are the site owners legal obligations with regard to additional protection in addition to each home owners RCD? Mobile home parks are fed from a TT system. In other words what protects...
Have any of you ever come across a TT system that the earth fault loop impedance readings are as good as a TN, TNC-S system?
Ie, falling well within the maximum permitted value of the MCB?
If so, would you then still recommend RCD protection, If there is none?
Cheers
Hello All,
I am a new member with a question i hope you can help me with.
TT System, Ze test with main earth disconnected from earth bar reading = 195 ohms
Zs test on ring main reading = 0.68 ohms..!
Retested Ze but this time connected to the earth bar (main earth not connected to earth bar)...
Hi, at both my colleges TT was only ever briefly discussed and in the main it was TN-S and TN-C-S that was dealt with. The comment tended to be "You'll only ever see that in rural situations". I tried suggesting it's applications in outbuildings even where the main source was TN=S/TN-C-S but it...
Hi new here :-)
Can anyone suggest how I can improve my Zs readings on a TT system for my final cct's.
Already have split board with 2 x 30ma RCD's and type B breakers!
A Should I be changing to RCBO's?
B try adding more earth rods! dont fancy this as problematic...
C what can you suggest...
Instaled swa cabling to 2 portacabins,made it tt system,all cabins r tested wiv usual rcd ctrl DBs,problem wiv the Ze offa the earth electode,the measured resistance was 275 ohms,iee recommends max 200 ohms,wot wud you guys do,by the way its a temporary installation cheers men ta ra bab
Hi all, hoping some 1 out there can help me on the following problem. just recently qualified and have this nightmare situation with no experience on the following problem.
I have nuissance tripping on a 30mA RCD. it trips at random times and can go as long as 5 days before it goes again. the...
Sorry guys need help with this one,
In 12 years of being a sparks i never come had to deal with TT systems, and for the life of me can remember all the stuff i learnt back in the day and can't find any of my notes from college.
CU methods=
1. 100ma (delayed/slugged) main switch, with 30ma...
I am testing my garage which has a TT system. I have a 30mA RCD as a main switch but am having problems with RCD testing using my Megger 1720. I have a Ze of 196 ohms which I know is OK so began testing the RCD. When I come to a x5 test it will not test because it tells me I have a touch...
Hello everyone,
Have been inspecting caravans statics at a 200+site. The levels of ZE are 8+ ohms at the caravan hook up and it is on a TT system (the incomming mains) to 4 or 5 submain distribution points where there is a common earth rod and from there via swa using the cable core or armourmed...
Upon doing a consumer unit upgrade + installation test today I came accross an unusal fault. I did all the usual dead tests and everything was fine, but when doing a Zs on the boiler/lighting/ring main circuits they all came back as reverse polarity. The first thing that came to mind was having...
HiCan anyone help me with regards to filling in a niceic part p cert with regards to the part were it concerns tt.This is on page 2 I need help with the parts electrode resistance ra , is this the measured ze result I have taken ?And also method of measurement ? Also what is the maximum ze for a...
im intending to carry out a c.unit upgrade on a domestic property, no earth provide by supplier so its a TT system,no electrode seems to be visible or present
but there is a reading there something like 5ohms could be a buried rod/rods somewhere or connected to old service pipe, going to...
hi
doing an extention of a tt system via a henely block, 50a fused switch, 16mm cable into a seperate cu. i want to discriminate between rcd's and cu's.
my question is do i connect the earth from the 16mm cable into a m.e.t then to earth rod, or just connect it to the fused switch or into the...
Massive site in deep rural kent few big dwellings, swimming pool etc etc
there is an outer building/shed/store (not sure of use) room on the site as well
there has been a seperate feed brought down off the overhead line into this little box built (to house cut outs and meters for all the...
I've recently completed a part p defined scope course but all of our testing was on TNS or TNCS systems, in our house we have a TT system and in the OSG I can't find much information on the maximum earth fault loop impedence, just says that it is likely to be higher than their TN tables? I might...
If a High Integrity CSU where every circuit is protected by a mix of RCDs & RCBOs is connected to a TT system, is it still necessary to fit a 100mA S front end RCD?
Hi i was wondering what the downside to connecting the earth to an earth rod TT system AND to the TNCS from which the supply is being fed from, i understand that in the fault of the pme neutral going down that a caravan could become live under fault conditions but surley 2 earth paths would be...
Can a Sunnyboy SB3800 inverter disconnect on a TT system fast enough to prevent injury through shock?
The installation has an RCD fitted and the inverter is connected to a 16 amp MCB.
With the inverter having simple separation, does this negate the need for an RCD to protect the cable...
Went to put in a new circuit (for a solar inverter) on a property with a TT system (the first time I've encountered one). The existing system is a dog's breakfast with three splits at the after the meter at a Henley block. There's some kind of 60 amp breaker labelled BS 842 in the mix. This may...