Hi all
Odd one today .. all 6 Hager rcbo's in a tn+n db have the test buttons not working..
But when tested with a multifunctiontester they react fine..
Now..I guess I'm going to have to fail them..even though they work fine.
Hager technical say they have never heard of this.
Db is in a plant...
Hello,
Last year I had a double socket (1) put in my room which was spurred off the ring main by a registered electrician.
This year, another company : -
i) installed two double sockets (2) and (3) either side of (1) and made the connection with flex wire
ii) left the blue and brown wires...
Amnesh Singh submitted a new resource:
18th Edition MINOR ELECTRICAL INSTALLATION WORKS CERTIFICATE - 18th Edition MINOR ELECTRICAL INSTALLATION WORKS CERTIFICATE, July 2018.
Read more about this resource...
Posted this in the wrong section:
We had our electrical engineer talk to us all later week regarding testing. It was agreed that if you were to install a spur socket for example then you only test the leg you have installed. This strikes me as not correct. I would have thought the entire...
Just a quick one.. I have been to a job today where the shower isolator switch had burnt out, as it wasn't RCD protected I replaced the switch with a 1 way consumer unit with an RCD.
My question is..do I need to do a full EIC or would a minor works do?
Cheers
Job is to install a spur of a RFC. Once installed I will issue minor works as should be done.
However, I was thinking, the r1+r2 value reading/test, is that from the spurred point or from the board?
Also another job I have is to replace some floor sockets that have been damaged. Sockets are on...
Just carried out an EICR on a standard semi which has had some work done in 2015-16. The works included connecting an outbuilding to the rear of the house to create a hall, WC and utility room. The Kitchen was also replaced, new cooker and shower circuits installed.
The 1 sockets circuit does...
hello guys
Garden brick lights all need replacing as they are waterlogged.
Client paid for me to fault find and the existing cabling gave plus 2 meg ohms so the cabling appears to be healthy.
Question client has asked is what guarantees I give.
I normally give 5 years on cabling I have...
Having recently passed Domestic installers exams but not having set up a business or not yet working for an electrician, if i do some minor work for a family member, can i issue them with a Minor Works certificate i.e. with no company name on the document?
Just your thoughts on this one,doing a part refurb on existing offices,no initial verification or certs found anywhere.
Premises rewired bout 1990,adding sockets here & there in each room.
The DB is a Crabtree Tpn polestar,just finished some loop readings ,& not good,1.49 the highest,there is...
Hi everyone, hoping someone can help me with a little puzzle.....
I have an inline extractor fan servicing 3 bathrooms which has stopped working. Called a (proper) electrician who couldn't find any faults and suggested replacing the whole extractor fan unit. Before doing so I had a quick look...
Hi there, just trying to find out some info regarding the issue of a minor works cert.
Having recently completed the 2395 course, I can carry out periodics, but wondered if I can issue a minor works cert or whether I have to wait until I have done my 2394 course ? Many thanks
:)
Hello guys
short and simple, wifi hub downstairs with weak signal reaching the 3rd floor.
I have not used a booster that utilizes the final socket circuit cabling before, are they any good or would anyone recommend something else?
Interested in fellow sparks opinions on this.
Client of a 15-20year old commercial/Industrial premises wants an additional 13a socket outlet installed for a specific piece of equipment, the additional wiring for this will be off a current non-rcd ring (with satisfactory Zs value) and installed...
Hi gents,
I'm working on a container thats is ply lined and has lighting and power inside all run in plastic 20mm surface conduit. Protective device is a garage 2-way consumer unit with 30ma rcd main switch (already installed on arrival). The container is in middle of a field on a mod site -...
hi all, currently doing an office refurb and are ready to reinstate switch drops that were removed to allow walls to be taken down. The wiring is all T&E into klik plug in boxes above the ceiling. Currently having a discussion on site with another electrician about how we go about doing our...