You need to test them properly.
Accurately measure the resistance of exactly 1M of conductor, preferably using something like a ductor/milliohmmeter with a reasonable test current if you have access to it or else pass a current of say 25A through it and measure the volt drop to get the resistance. Then cut the conductor and join it with a through crimp using that tool. Then re measure the resistance of 1M including the joint using the same tester/method.
The results should be substantially the same, if not then you have a high resistance joint.
You can calculate the heating effects of this increase in resistance using the current that the cable is likely to be used to carry. for example if you use 16mm conductor and the joint adds 2 ohms resistance to the conductor your heating effect with 63A current would be
P = I[SUP]2[/SUP]R
P = (63Ax63A)x2ohm
P = 7938W
P = 7,9kW