giddash

Hi there,
I did wired 10.5kw shower with a 10mm cable on a 40A breaker for an old lady's bathroom.she recently got a builder in to do some tiling work and this guy thinks the wiring is wrong and that i should have use 45A breaker else the house will catch fire.I don't think his is right as there no way this could happen as I did test the breaker and it tripped in less than 5s but tought i should post this any way.
 
It seems like you on the limits here mate, all depends on reference method the cable is installed. There is no way it will catch a fire,using lower rating mcb you just increased protection for the cable, builder talking nonsense, if anything , if you increased mcb to 45A , you increase the risk of fire.
In any way I am not saying that your design is up to scratch without knowing details, and yes , not sure how you tested mcb?
 
Don't understand the post at all, you do a basic install perform the required calculations to determine the correct cable size and breaker rating, once installed you tested circuit and issued paperwork and notified lbc, and then a tiler turns up and says you've done it wrong???.

Or happen you just guessed the cable size and breaker rating / didn't bother notifying the lbc and took the money?.

Whichever one it is it just doesn't sound like you know what your doing, if you did you'd check your books if you were that concerned, not post on a forum.
 

Reply to 10.5kw shower wired in 10mm twin n earth on a 40A breaker a problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
923

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top