giddash

Hi there,
I did wired 10.5kw shower with a 10mm cable on a 40A breaker for an old lady's bathroom.she recently got a builder in to do some tiling work and this guy thinks the wiring is wrong and that i should have use 45A breaker else the house will catch fire.I don't think his is right as there no way this could happen as I did test the breaker and it tripped in less than 5s but tought i should post this any way.
 
i see downrating of MCB's quite alot, wouldn't even code it tbh. i wouldn't design it like that either, whenever i find it it's been like that for years and you know the old saying, if it aint broke don't fix it. if i remember correctly a modern MCB will trip at 1.45 times the rated current. so thats 58A for a 40A breaker, i think it will be alright
 
Testing an mcb is like seeing how long your tent would cope for in a Hurricane,
Apply a 150 mph wind and the tent gets destroyed after staying up for a second
The tent may have passed the test, but its not a lot of good for sleeping under again lol

And these shower ratings are sometimes a bit of an exaggeration
 
im considering putting my 10.5kw shower on a 40a rcbo, 1 because they dont do bigger in crabtree and 2 because i dont want to buy a seperate shower unit of 63a rcd with 50a mcb....if it trips then ill have to change it but if anything its safer.......

- - - Updated - - -

im considering putting my 10.5kw shower on a 40a rcbo, 1 because they dont do bigger in crabtree and 2 because i dont want to buy a seperate shower unit of 63a rcd with 50a mcb....if it trips then ill have to change it but if anything its safer.......
 
davewdave;748232]im considering putting my 10.5kw shower on a 40a rcbo, 1 because they dont do bigger in crabtree and 2 because i dont want to buy a seperate shower unit of 63a rcd with 50a mcb....if it trips then ill have to change it but if anything its safer.......

I can't understand why anyone would even consider installing a 10.5 KW shower, let alone actually installing one!! lol!!
 
I can't understand why anyone would even consider installing a 10.5 KW shower, let alone actually installing one!! lol!!
its a modern phenomena eng called `my showers bigger than yours` at the neighbours...
a bit like the `chicken brick` that used to be sold by habitat back in the late 70s early 80s...so all the street would come round to admire it...a stoneware pot you cooked a chicken in...
anyway...the point is some feel the need to have the best kitchen, biggest shower,sparklyest bathroom etc...
these people need patience and understanding.....
 
its a modern phenomena eng called `my showers bigger than yours` at the neighbours...
a bit like the `chicken brick` that used to be sold by habitat back in the late 70s early 80s...so all the street would come round to admire it...a stoneware pot you cooked a chicken in...
anyway...the point is some feel the need to have the best kitchen, biggest shower,sparklyest bathroom etc...
these people need patience and understanding.....


They need a good kickin Glen......My wife is exactly the same, she has to have better than my cousins missus.....She needs a good kickin aswell!!lol
 

Reply to 10.5kw shower wired in 10mm twin n earth on a 40A breaker a problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
923

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top