Morning everyone,

Hope your all well.

Just a a quick question. We have been asked to quote for a HMO conversion, in a domestic property. So basically, the developer buys these houses and makes rooms out if them.
Leach room is basic, small ensuite shower ( not electric ), lights and a few sockets. There is a communal kitchen and each room is supplied by its own consumer unit.
There are 2 circuits, lights and sockets.
What I'm asking is, the consumer units are fed via 10mm T&E that go down to 60A isolators, which in turn go into a big Henley block.
There are about 5 rooms, so five isolators.
I would have thought that the consumer units for each room , from the isolators had have 16mm earth ?
Obviously things like communal smokes and fire alarm system etc are fed from landlord board.
The supply is a TN-S single phase

regards,
sav
 
Ok. The set up his current electrician has is as follows

single phase TNS 100A BS1361. Tails into single meter.
From there into Henley blocks using 25mm tails.
From Henley blocks, 25mm tails into Mk60A isolator.
From isolator 10mm T&E ( presume buried in wall & under floor etc into consumer unit.
Consumer unit has 30ma RCD main switch and 2 circuits. Lights and sockets.
I also would have though swa from isolator into consumer unit.
But I would use 16mm ??
bonding as far as I could see is main gas and water in 10mm. I couldn't see an earth from the metal isolators to the MET though. Also couldn't see any supplementary bonding in the rooms. That's why the alarm bells rang in the head.
But I don't think 10mm T&E is the way to go ?
Sav
 
Morning everyone,

Hope your all well.

Just a a quick question. We have been asked to quote for a HMO conversion, in a domestic property. So basically, the developer buys these houses and makes rooms out if them.
Leach room is basic, small ensuite shower ( not electric ), lights and a few sockets. There is a communal kitchen and each room is supplied by its own consumer unit.
There are 2 circuits, lights and sockets.
What I'm asking is, the consumer units are fed via 10mm T&E that go down to 60A isolators, which in turn go into a big Henley block.
There are about 5 rooms, so five isolators.
I would have thought that the consumer units for each room , from the isolators had have 16mm earth ?
Obviously things like communal smokes and fire alarm system etc are fed from landlord board.
The supply is a TN-S single phase

regards,
sav
cant see myself renting off this fella though....
 
this keeps cropping up does this.

inappropriate cable type for the proposed feeders

as Murdoch has quite rightly pointed out the way forward here is SWAs with bottom end additional protection for finals...
 
63A cut out for a DB supply with only a socket and light circuit?? What's the max demand of each unit, 20A? I'd be looking at maybe a 20A MCB in a DB at the origin then on to a local two way RCD DB fed via SWA sized accordingly with a 16A for the sockets and a 3A for the lights. Will each unit be seperately metered and if so, will that be a suppliers meter or a private landlords meter?

As others have said there is far too much we don't know to provide accurate advice so I'm only speculating, one thing is for sure though and that is this installation needs some proper thought out design. Slinging in 63A switch fuses and T+E submains just doesn't cut it I'm afraid.
 
16mm for 1 sockets & 1 lights circuit ?

do me a favour , the existing 10mm is already hideously over rated as it is for what will unlikely be more than 20A per unit after diversity

4 or 6mm t&e subs in pvc trunking to each bedsit is the sort of cost savy design you should be considering.
 
63A cut out for a DB supply with only a socket and light circuit?? What's the max demand of each unit, 20A? I'd be looking at maybe a 20A MCB in a DB at the origin then on to a local two way RCD DB fed via SWA sized accordingly with a 16A for the sockets and a 3A for the lights. Will each unit be seperately metered and if so, will that be a suppliers meter or a private landlords meter?

As others have said there is far too much we don't know to provide accurate advice so I'm only speculating, one thing is for sure though and that is this installation needs some proper thought out design. Slinging in 63A switch fuses and T+E submains just doesn't cut it I'm afraid.


a 20mcb at the start wilpl trip at same time as 16 if a fault occurs
 
Some partial discrimination between the upstream ocpd and the final circuits imo would be a good thing here, especially if the incomers are some distance from the flats.
And in this instance an HRC fuse (Switch fuse) to MCB in CU, would be better than MCB to MCB.

Infact, if your not worried about OCPD discimination and the posibility of the upstream device (MCB) operating under fault conditions on a flats final circuit, why worry about a front end RCD being installed?
 
Last edited by a moderator:
The OP could go for 45A HRC fuses then, I still think it's overkill though, especially cost wise. How many short circuit faults are we anticipating will occur?

Front end RCDs are bad for a whole host of reasons as they trip under many different conditions.
 

Reply to 10mm T&E for Consumer unit supply in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
312
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
730

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top