Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.
Supply to property TN-C-S
Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)
Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.
Earth rod with 10mm to the RCD spur and TT the rest.
Any advice would be great
you will probably find out from the tub supplier/manufacturer that it come with an integrated 10mA RCD in the mains lead. i get the VD on 4.0mm to be 4.3V so it's adequate for the job. ( 11 x 13 x 30 )/1000.
It will be Sat on decking with around 2/3ft surrounding before it turns to grass again
Never done one myself, but it’s a common question raised on here. As said, I read before that some advise with pms supply, to use supply earthing facility AND rod near tub.
Perhaps more learned members can comment on that?
Read a best practice guide on hot tubs which said TT it so I've done that on the few that I've done since.
Having come off the phone to a American bloke who could not not me the power raiding except it pulls 12.8 amps when pumps start.
My installation
16amp mcb from CU to a rcd ip enclosure with rcd fitting inside (drop pme at this point)
Pick up new TT earth
To 25amp rotary is lsolator to the hot tub
Tescos and BM seem to selling a lot of LayZspa hot tubs at the moment.
The Hot tub itself is inflatable, like a large paddling pool.
The pump/heater/bubble maker is a separate unit with quite a long lead which has a 10mA in line RCD.
The pump unit is waterproof, though I have not found an IP rating. The unit has to be next to the tub to connect the pipework and so the controls can be reached.
Manchester
13amp Hot tub supply
HRM-ELEC,
UNG,