Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.

Supply to property TN-C-S

Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)

Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.

Earth rod with 10mm to the RCD spur and TT the rest.

Any advice would be great
 
This is what I was doing Easter weekend:
975F396B-143B-4E7F-9389-D058341AADF1.jpeg
 
i'm more concerned about the bird cage on the wall. how do they get in and out?
 
I do feel these 'like, dislike, agree etc etc' icons create more negative responses, than they set out to achieve.

I mean, why is there a 'bad spelling' icon. Do I need some **** on here to tell me, when someone has posted a reply with incorrect spelling & grammar??

I could of said, 'I mean, wheir is their a 'bid spelling' icen. Do I nead some twot on hear to till me, when someone has pisted incurrect spilling & grammer'. :D

I have always said the same thing. They are a waste of time and just starts slagging off comments. I'd get rid of them if it was up to me, but the powers that be seem not to care but whinge when there is fighting in threads.
 
Last hot tub (last year) I fitted, I put a separate CU the house next to the main CU which had spare ways but they were on a split load board so I didn’t want any nuisance tripping in the house, I installed a supply to the tub with a rcbo on supply end used 6mm three core SWA at the hot tub end I installed an IP65 lock off isolator switch then the last five metres used 6mm three core flex (can’t remember the VV code for the flex)
 
Thing with these hot tubs, is you have to use chlorine, continuously heat and circulate the water and clean the filter daily.

You can use Bromine it is a lot more pleasant than chlorine and doesn't rot the tub and equipment.
Seen both chemicals used over the last 15 years and tubs used with chlorine generally have never ending repair bills from regularly replacing valves, seals, heaters and pumps etc.
Tubs used with bromine do seem to last longer before major repairs are needed
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
13amp Hot tub supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
57
Unsolved
--

Advert

Thread statistics

Created
HRM-ELEC,
Last reply from
UNG,
Replies
57
Views
7,143

Advert

Back
Top