18th edition and the requirement to upgrade consumer units when electric hobs are replaced

Good morning

does anyone know about anything in the 18th edition and the requirement to upgrade consumer units when electric hobs are replaced?

i had a customer ask me about it this morning.

Many thanks
Simon
 
Hi Simon and Welcome to the Forum :) .
No changes to fixed wiring are required by BS7671 when appliances are replaced. However, the detail here is the new cooker’s manufacturer may state something in their installation instructions that needs to be considered.
 
They might be confused regards the fitting of RCD’s when adding to circuits.
 
I am going to replace a consumer unit this afternoon thanks to an induction hob being installed..
The extra earth leakage on the installation from the hob causing the RCD incomer to trip..
So they may be recommending a cu change based on this kind of scenario
 
I am going to replace a consumer unit this afternoon thanks to an induction hob being installed..
The extra earth leakage on the installation from the hob causing the RCD incomer to trip..
So they may be recommending a cu change based on this kind of scenario

So what’s going to stop the hob tripping it’s circuit Rcbo after the CU change?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
simon James,
Last reply from
Deleted member 26818,
Replies
20
Views
3,291

Advert

Back
Top