ch1cki
Any ideas??
I've had a job like this before. very small industrial unit with tranny 5 meters away. PFC was over 20ka, the mcbs in the DB were only rated to 6 ka. main fuse was 100a 1361. in gn 3 it gives info on this situation. so basically in short we changed the board so we could install 16ka mcbs as gn 3 advises and all was good. you need to have the right type of main fuse for this to work. I'm sure someone is going to tell me this is overkill but I'm standing by it.
The conditional rating is 16ka as I posted
way back but if your PFC was 20KA, why did you install devices rated at 16KA?
Could be underkill!