19.1ka psc reading on a 2 bed small house!

I'd also expect the impedance of the transformer winding plus the impedance of the suppliers cable to be at least 0.02 Ohms but as we know, our testers can't work accurately at those values.
 
If the tails have been unnecessarily upgraded that will consequently increase PSCC and PEFC; and if the earthing conductor has been unnecessarily upgraded that will also increase PEFC.
 
If the tails have been unnecessarily upgraded that will consequently increase PSCC and PEFC; and if the earthing conductor has been unnecessarily upgraded that will also increase PEFC.

Yep!! It's always been a fine line in getting distribution systems/layout cables correctly sized, to deliver the desired load requirements, whilst at the same time limiting PSCCs etc!!!
 