Any ideas??
PEFC was the higher value i would just like to know how to bring them down?
PEFC was the higher value i would just like to know how to bring them down?
True, which is normally the higher?Everyone is concentrating on the earth loop, PFC is 2 tests, the PSSC remains constant regardless of the earth loop!
True, which is normally the higher?
How's that Donkey coping with the fence?Well it depends on the system but if the transformer is so close then TN-S or TN-C-S I would expect to have very similar measured values for PEFC and PSSC.
not add an earth rod, get rid of pme!
If the tails have been unnecessarily upgraded that will consequently increase PSCC and PEFC; and if the earthing conductor has been unnecessarily upgraded that will also increase PEFC.
how do you measure PSCC then?