Just wondering what folks would do if you came across this on your travels. 4mm radial sockets circuit, on 32A MCB. Two branches from the CU, one supplying 6 double sockets, wired entirely in 4mm, so fine. The other branch consists of a 1m run of 4mm to a double socket, then around 5m in 2.5mm cable on to a second double socket.
The question is, who would be happy to leave this arrangement in place, and who would downgrade the breaker to 20A? I would say it's ok, as the 2.5mm can't be overloaded as it feeds only one double socket, just like an infused spur off a ring.
As somebody said before, its shown as an example in figure 15B, so why is C2 or wrong or poor practise?
Fig 15B sure does show it, no question. My take is ...
Fig refers to 433.1, but 433.1 doesn't lead me to think 4mm to 2.5mm is ok. But reading on to 433.2.2, it seems to say ok < 3m, with a couple of conditions.
The op asked for opinions, mine you have two final circuits from a single protective device one of which reduces in csa. This circuit which reduces in csa is ad hoc with absolutely no thought for BS7671, the chance of further add ons with the same sized reduced cable is high.
I don't agree with not having a circuit such as this because people might add further sockets on in the future. If you go with that theory then you would never have spurs from sockets at all, because someone might come along and spur from the spur. No difference - both cases have a length of 2.5mm feeding a socket. Daz
Th
The chances of this so called spur being installed as per BS7671s "Guidance" is zero, I would feel it is open to further abuse, that is how I view it.
interesting, 'cause its clearly okay in App. 15. perhaps the intention is 433.3.1 (ii), where a single outlet is deemed "not likely to carry overload current" ?
Is it me or is this getting all out of proportion?
No its not necessarily how any of us would install it, but its not likely to be an issue either. Its highly unlikely the circuit would be overloaded during normal use, and any electrician worth his/her weight would not install another spur off that socket.
I would maybe just make a note on the report and possibly give it a C3/C4 if I felt the installation required it.
By coincidence just finished doing a school EICR, existing circuit has a spurred two gang and just recently another has been connected from it. All fine according to "electrician" who also left a MWC on site.
That's down to that bad boy then. Most things plugged into sockets nowadays aren't 2kw electric fires.
what if somebody plugs a 4 gang into the last socket??? easily overloaded then sir
Things can happen, no doubt. But it is very unlikely that during normal use in a domestic property that the socket in question would be overloaded. If some idiot decided to extend off that socket then that's their responsibility. No one can foresee all events.
Like I said non of us would install the socket in this manner, and yes in exceptional circumstance there could be a chance it gets overloaded. As I said I would asses the install, make a note on the report and then perhaps code it accordingly if I felt it was going to be a potential problem.
Its easy to fall into the nanny state mentality, stifled by bureaucracy. This doesn't mean ignoring potential hazards, but rather accessing the situations to determine the severity. But we cannot wrap people up in cotton wool, they have to take some responsibility for their own welfare.
Reply to 2.5mm on 32A MCB in the UK Electrical Forum area at ElectriciansForums.net
Haha yes, it is. Must be a northern expression. Have a Google 😂