kingeri

-
Arms
Joined
Apr 13, 2012
Messages
2,598
Reaction score
1,362
Location
Yorkshire
Just wondering what folks would do if you came across this on your travels. 4mm radial sockets circuit, on 32A MCB. Two branches from the CU, one supplying 6 double sockets, wired entirely in 4mm, so fine. The other branch consists of a 1m run of 4mm to a double socket, then around 5m in 2.5mm cable on to a second double socket.

The question is, who would be happy to leave this arrangement in place, and who would downgrade the breaker to 20A? I would say it's ok, as the 2.5mm can't be overloaded as it feeds only one double socket, just like an infused spur off a ring.
 
As somebody said before, its shown as an example in figure 15B, so why is C2 or wrong or poor practise?

Fig 15B sure does show it, no question. My take is ...
Fig refers to 433.1, but 433.1 doesn't lead me to think 4mm to 2.5mm is ok. But reading on to 433.2.2, it seems to say ok < 3m, with a couple of conditions.
 
The op asked for opinions, mine you have two final circuits from a single protective device one of which reduces in csa. This circuit which reduces in csa is ad hoc with absolutely no thought for BS7671, the chance of further add ons with the same sized reduced cable is high.
 
I don't agree with not having a circuit such as this because people might add further sockets on in the future. If you go with that theory then you would never have spurs from sockets at all, because someone might come along and spur from the spur. No difference - both cases have a length of 2.5mm feeding a socket. Daz
 
Th
I don't agree with not having a circuit such as this because people might add further sockets on in the future. If you go with that theory then you would never have spurs from sockets at all, because someone might come along and spur from the spur. No difference - both cases have a length of 2.5mm feeding a socket. Daz
The chances of this so called spur being installed as per BS7671s "Guidance" is zero, I would feel it is open to further abuse, that is how I view it.
 
Fig 15B sure does show it, no question. My take is ...
Fig refers to 433.1, but 433.1 doesn't lead me to think 4mm to 2.5mm is ok. But reading on to 433.2.2, it seems to say ok < 3m, with a couple of conditions.

interesting, 'cause its clearly okay in App. 15. perhaps the intention is 433.3.1 (ii), where a single outlet is deemed "not likely to carry overload current" ?
 
Is it me or is this getting all out of proportion?
No its not necessarily how any of us would install it, but its not likely to be an issue either. Its highly unlikely the circuit would be overloaded during normal use, and any electrician worth his/her weight would not install another spur off that socket.
I would maybe just make a note on the report and possibly give it a C3/C4 if I felt the installation required it.
 
Is it me or is this getting all out of proportion?
No its not necessarily how any of us would install it, but its not likely to be an issue either. Its highly unlikely the circuit would be overloaded during normal use, and any electrician worth his/her weight would not install another spur off that socket.
I would maybe just make a note on the report and possibly give it a C3/C4 if I felt the installation required it.
By coincidence just finished doing a school EICR, existing circuit has a spurred two gang and just recently another has been connected from it. All fine according to "electrician" who also left a MWC on site.
 
By coincidence just finished doing a school EICR, existing circuit has a spurred two gang and just recently another has been connected from it. All fine according to "electrician" who also left a MWC on site.
That's down to that bad boy then. Most things plugged into sockets nowadays aren't 2kw electric fires.
 
Just wondering what folks would do if you came across this on your travels. 4mm radial sockets circuit, on 32A MCB. Two branches from the CU, one supplying 6 double sockets, wired entirely in 4mm, so fine. The other branch consists of a 1m run of 4mm to a double socket, then around 5m in 2.5mm cable on to a second double socket.

The question is, who would be happy to leave this arrangement in place, and who would downgrade the breaker to 20A? I would say it's ok, as the 2.5mm can't be overloaded as it feeds only one double socket, just like an infused spur off a ring.
what if somebody plugs a 4 gang into the last socket??? easily overloaded then sir
 
By coincidence just finished doing a school EICR, existing circuit has a spurred two gang and just recently another has been connected from it. All fine according to "electrician" who also left a MWC on site.
Things can happen, no doubt. But it is very unlikely that during normal use in a domestic property that the socket in question would be overloaded. If some idiot decided to extend off that socket then that's their responsibility. No one can foresee all events.
Like I said non of us would install the socket in this manner, and yes in exceptional circumstance there could be a chance it gets overloaded. As I said I would asses the install, make a note on the report and then perhaps code it accordingly if I felt it was going to be a potential problem.

Its easy to fall into the nanny state mentality, stifled by bureaucracy. This doesn't mean ignoring potential hazards, but rather accessing the situations to determine the severity. But we cannot wrap people up in cotton wool, they have to take some responsibility for their own welfare.
 

Reply to 2.5mm on 32A MCB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
336
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top