If you for instance were to run a cable with no joins, directly from a CU to to a double insulated item of equipment, how many points in the wiring requiring a CPC to be connected would there be?
If no accessories are used in the circuit (remembering that an item of current using equipment is not considered to be an accessory) where would you connect a CPC?

Can't think of anywhere that I could connect the cpc to, other than a wago or the terminal of the back box ( if applicable). In the fan itself I would sleeve the cpc and terminate it in a floating wago, or crimp, or screw type terminal block.

Of course it is impossible to earth a piece of plastic, but if the Regs say I must run a cpc to it, then I must comply, whether it makes sense or not......
 
spinlondon is talking sense. To avoid bad job relations with the tester, change the cable to 3core but make sure you insulate the end of the cpc after sleeving it, or better still over-sleeve it. You are perfectly correct installing the 2core, but the tester is trying to be pedantic and perhaps over-zealous. Refer to your supervisor discretely if that's possible. The label is a good idea, i.e. class ii equipment - no cpc required. There will be no where to connect a cpc any how except in the termination box of the local maintenance switch.
Cheers
Les
 
If you take this BS7871 regulation literary, that a CPC should always be taken to any class11 accessory, Then you have to ask ''Why'' do all the manufacturers of class11 equipment that supply a factory fitted lead/cable only ever provide that lead/cable with a 2 cores?? lol!!
 
Using 3 core for class II items such as downlights and fans is a bad idea in my view, it's why we so often see CPCs just cut off and not terminated - cos there's nowhere to terminate it to.
 
spinlondon is just too cool for school

on a realistic point this two core cable where would you get it from? left over under cupboard light cable?

do you think there was a slight debate in the 60s regarding 2 core cable because at the time the fashion was wooden backs,
 
Ive got some 2 core flex on my van, use it to extend pendants in houses with high ceilings, I suppose we could run it to a table lamp in a restaurant through some soil with plants in it like they do in spain.
 
How can the tester get an r1+r2 reading? its good practise to continue the cpc even though the the item is double insulated. I was taught that you need an cpc to make it easier to test and also to allow for future references i.e change for a metal item at a later date, also live and neutral conductors needs to be the same size. (just in case single and earth was used)
 
Its a bit ambiguous really, i read it as the cpc must not be connected to an ECP unless catered for, not you can't terminate in a floating wago, as long as it is marked as a cpc
 
If you were to park the CPC in a 'wago' would the 'wago' not then become an ECP, one that was not catered for?
Or in other words not specifically provisioned for in the specifcation for the equipment concerned.
 
Technically yes, but that would mean we would have to put either a maintenance free enclosure to terminate the cpc in and then 2(3) core flex to the fan or an ip44 enclosure near to the fan then flex to the fan, we wouldnt get any work done:frown2:

Out of interest, how do you terminate your domestic fan feeds?
 
It's not something that I've come across in domestic installations to that extent, as the fans I use are either SELV or 230V wired with 3core&E.
However, with a bell transformer for instance, I would normally just take 2 cores to the transformer.
Where I've installed class II equipment in commercial or industrial installations, I generally take a CPC to a JB or enclosure near to the equipment, park it, then run 2core to the equipment.
However, there have been times when I've not had that option, and following instructions, have cut the CPC out of T&E or 3core flex then terminated in the class II equipment.

In many instances running a CPC to and parking it in the enclosure of an item of class II equipment is not going to make a blind bit of difference.
The likelyhood of the CPC becoming loose and shorting against a live conductor is just the same for Class II equipment as it is for Class I equipment.
However if that CPC were to come into contact with an exposed-conductive-part it could introduce a difference in potential.
Something that may not be desired if the equipment is installed in certain locations.
It could even allow fault currents from a fault elsewhere in the installation to enter a location where such currents could be present a danger.
 
412.2.3.2 "Except where Regulation 412.1.3 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory."

412.2.2.4 "No conductive part enclosed in the enclosure shall be connected to a protective conductor.......Inside the enclosure, any such conductor and their terminals shall be insulated as though they were live parts, and the terminals shall be marked as protective conductor terminals

No exposed-conductive part or intermediate part shall be connected to any protective conductor unless specific provision for this is made in the specification for the equipment concerned"


The first Reg says I have to run a cpc to the fan. Fair enough. Can't see how the second Reg prevents me from terminating the cpc in a wago or terminal block.

Am I missing something?


 
As a connector block or wago is not an exposed conductive part, or part of the equipment at all (merely living in a cavity inside it), then this doesn't count as connecting a CPC to something in a Class2 device.
 

Reply to 2 core cable.. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
564
dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
472
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
217
Ok I’ll try this when I’m down
Replies
4
Views
285

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks