2 core cable.. | Page 2 | on ElectriciansForums

Discuss 2 core cable.. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

412.2.3.2

412.2.3.2 Except where Regulation 412.1.3 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory.
 
412.2.3.2 Except where regulation 412.1.3 applies, a circuit suppling one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory

Still think its good practice to always have a CPC available.
 
Just flicking through now fella, looks like your right unless I spot a small reg hiding under another somewhere haha, my feet are cold now as well lol, I ran out to the van with no socks on
 
Yet another daft example of the regs.

Why don't they simply say that all circuits from a distribution board must have a continuous CPC run to each and every accessory??
 
So in summary it seems that

"412.2.3.2 Except where Regulation 412.1.3 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory."

supercedes "411.3.1.1"

and thus the tester was correct on this occasion?
 
yep dedication, basically it is about time a decent chat was on here by sparks discussing a reg or 2, after having a good look through, I think murdoch is right, reg 412.2.3.2 looks like the reg which suggests it is required, still looking for the hidden one though.
 
412.2.3.2 Except where Regulation 412.1.3 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory.

That's it - with the note that it is intended to take account of the possible replacement by the user of class II equipment by class I equipment.

The proviso of 412.1.3 relates to whole installations of class II under supervision so that no changes will be made - plus a bit more.


Edit - I type too slow.
 
If you for instance were to run a cable with no joins, directly from a CU to to a double insulated item of equipment, how many points in the wiring requiring a CPC to be connected would there be?
If no accessories are used in the circuit (remembering that an item of current using equipment is not considered to be an accessory) where would you connect a CPC?
 
If you for instance were to run a cable with no joins, directly from a CU to to a double insulated item of equipment, how many points in the wiring requiring a CPC to be connected would there be?
If no accessories are used in the circuit (remembering that an item of current using equipment is not considered to be an accessory) where would you connect a CPC?

Can't think of anywhere that I could connect the cpc to, other than a wago or the terminal of the back box ( if applicable). In the fan itself I would sleeve the cpc and terminate it in a floating wago, or crimp, or screw type terminal block.

Of course it is impossible to earth a piece of plastic, but if the Regs say I must run a cpc to it, then I must comply, whether it makes sense or not......
 
spinlondon is talking sense. To avoid bad job relations with the tester, change the cable to 3core but make sure you insulate the end of the cpc after sleeving it, or better still over-sleeve it. You are perfectly correct installing the 2core, but the tester is trying to be pedantic and perhaps over-zealous. Refer to your supervisor discretely if that's possible. The label is a good idea, i.e. class ii equipment - no cpc required. There will be no where to connect a cpc any how except in the termination box of the local maintenance switch.
Cheers
Les
 
If you take this BS7871 regulation literary, that a CPC should always be taken to any class11 accessory, Then you have to ask ''Why'' do all the manufacturers of class11 equipment that supply a factory fitted lead/cable only ever provide that lead/cable with a 2 cores?? lol!!
 
Using 3 core for class II items such as downlights and fans is a bad idea in my view, it's why we so often see CPCs just cut off and not terminated - cos there's nowhere to terminate it to.
 

Reply to 2 core cable.. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
229
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

What readings were you expecting for the cable prior to testing? What is the make of the protective device? Is there any previous paperwork [test...
Replies
3
Views
480
A problem putting multiple cores into a ferrule is when you need to do testing or fault finding. You can't just drop the ends out of the terminal...
Replies
2
Views
299

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top