I took the exam last night, i have a copy of it as well! Good luck every body that took it
Found it resonable. Heres my answers to dodgy questions in part A
Q2 - List 3 specific items of info regarding dnos equipment, made available to person doing an inital verification? Earthing arrangements, supply protective device charactersitics, and nominal voltage Uo
Q4 - 3 items to check when inspecting the erection and termination of new mineral insulated cables? no swarf in pot, insulation to outside of cable, no mechanical damage to outside (wasnt too sure on these answers)
Q6 b) - state two of the outcomes to be recorded following the successful completion of the continuity of ring final circuit test? continuity of ring final circuit conductors, and R1 + R2
Q7 - 3 tets following earth electrode for TT? earth fult loop impe, pfc, rcd testing
Q8 - one point connected to MET by cpc? socket
by main protective bond? metalic water pipe
earthing cond? distributors earthing facility
Q 11 - an insulation resistance test is to be carried out on a single phase 230v circuit supplying socket outlets with integral surge protection?
insulation resistance tester, 500v dc, 1.0 Mohm (it appers 500v dc is wrong)
Q 13 - a test is too be carried out between live conductor of a selv circuit and the conductors of a 400v 3 phase motor circuit to confirm electrrical seperation? insulation resistance tester, 500v dc, 1.0 M ohm
Q 16 - an earth electrode resistance test is to be carried out on an electrical installation, forming part of a TT system, using an earth fault loop impedance tester. State the action which must be taken prior to carrying out the test with regards to the-
supply to the installation - isolate from the installation
earthing conductor - disconnect from MET
and the action to be taken regarding the earthing conductor once a measurment has been made - subtract reading from result
Q 20 - state 3 possible consequences of a circuit breaker interuppting a fault current 3 x larger than its rated breaking capacity? it will be unusable again, it could cause a fire, it may cause damage to property and equipment
Let me know what you all think please