During the construction of an installation, insulation resistance tests have been carried out between live conductors and earth on the individual circuits and the L to E results are shown below. What is the expected value of insulation resistance L to E when the whole installation is tested?

1740752656925.png


can someone explain how to break down this question?

thanks
 
there is another with the answer

The insulation resistance of two circuits is of 40MΩ an 36MΩ respectively. When tested together what is the total insulation resistance:?

answer is 22mohms
 
Upvote 0
Bear in mind that when all the circuits are connected to the consumer unit, they are effectively in parallel. This should give you a clue as to how to answer the question.

Even without a calculator, there is one value that it will certainly be less than.
 
Upvote 0
During the construction of an installation, insulation resistance tests have been carried out between live conductors and earth on the individual circuits and the L to E results are shown below. What is the expected value of insulation resistance L to E when the whole installation is tested?

View attachment 119857


can someone explain how to break down this question?

thanks
1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4...
 
Upvote 0
Thanks alos there is a similar question here

The insulation resistance of two circuits is of 40MΩ an 36MΩ respectively. When tested together what is the total insulation resistance:?
Risteard gave the formula, which becomes:
1/40 + 1/36 = 1/R which to 2 decimal places is:
0.025 + 0.028 = 1/R
Work out R from that 🤔

Consider - if the two IR figures were both 40Meg, then in parallel that would make 20Meg.
But one is a lower resistance than 40, so your answer is going to be a lower number than 20.
 
Last edited:
Upvote 0
Risteard gave the formula, which becomes:
1/40 + 1/36 = 1/R which to 2 decimal places is:
0.025 + 0.028 = 1/R
Work out R from that 🤔

Consider - if the two IR figures were both 40Meg, then in parallel that would make 20Meg.
But one is a lower resistance than 40, so your answer is going to be a lower number than 20.
yes thanks makes sense now
 
Upvote 0
Risteard gave the formula, which becomes:
1/40 + 1/36 = 1/R which to 2 decimal places is:
0.025 + 0.028 = 1/R
Work out R from that 🤔

Consider - if the two IR figures were both 40Meg, then in parallel that would make 20Meg.
But one is a lower resistance than 40, so your answer is going to be a lower number than 20.
so with the 0.053 you then move that 2 decimal places?
 
Upvote 0

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
2391 question multiple choice IR help to break down
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
sid521,
Last reply from
sid521,
Replies
17
Views
406

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top