3.6kw oven on a 13amp plug top. | Page 3 | on ElectriciansForums
Discuss 3.6kw oven on a 13amp plug top. in the UK Electrical Forum area at ElectriciansForums.net
M
markthespark
Hello i have been asked to install an oven that is 3.6kw, i am wondering whether this would be fine plugged into a socket behind the existing oven taking into account diversity.
or whether i need to put it on its own radial supply.
Is there anyway of fusing a ring main down to 16amps?
Thanks.
I have an oven with a grill.
The grill is inside the oven.
Tidyboiler has never been able to grill my breakfast kippers at the same time as I'm roasting the pig for my dinner but last time she did grill my kippers the dozy bint burned them!!
It is either one or the other.
As usual it comes down to economics..is it cheaper to pay for someone to teach her to cook or cheaper to get a new model? (and I'm not talking about the cooker? :)
Like this?
[ElectriciansForums.net] 3.6kw oven on a 13amp plug top.
---- job chasing that socket in though....
That socket has got a 3 transformer 66KV sub behind it!!
So now the well proven diversity of cooker appliances shouldn't be taken into account, brilliant!! Cookers and/or ovens will generally be rated on the box (and within the manual) as ''connected'' load not ''Maximum'' load, so any elements within the cooker/oven than can't be used in tandem with other cooking elements shouldn't be included in the rating of what this oven can draw...
Why does this oven need to be fused at all?? You don't see any fuses provided on say a twin cooker connection plate. It's a fixed load so cannot overload, so providing the circuit supply is up to the job a 20A DP switch plate is all you need....
I have noticed most ovens that used to come already fitted with a 13Amp plug,now just have terminals for you to connect your own cable and I think there is a clue there (manufacturers are aware that a 3.6kw oven may work fine on a 13Amp plug ...for a while.) . When you go to cook Christmas dinner and the oven is working at full capacity for long hours then i would consider diversity to be a bit of a red herring mainly used by lazy and/or incompetent fitters, to avoid installing a new 20Amp radial,so they just throw it in a socket designed for 13 Amps max despite the appliance being capable of pulling 14 amps..!
A 3.6kw cooker needs a 4mm hofr (heatproof) cable from cooker to 20Amp isolation point,then feed isolation point in 4mm pvc twin + earth and protect circuit with 20Amp ocpd.
Have you ever seen what a 2kw heater can do to a plug top? Putting a modern oven on a plug is what you call sailing close to the wind
What do 2KW heaters do to plug-tops then? Daz
presumably they make 10 Amp fuses for appliances rated less than 10 Amps? Of which,an appliance which is rated at 14 Amps,is not such an appliance.
Sorry, I'm confused. What current would a 2kW heater draw?
I reckon between 8-9 Amps.
You seem to have quoted a 2kW heater and now jumped back to an oven when questioned about your statement that a 2kW heater melts a 13A plug top.
Reply to 3.6kw oven on a 13amp plug top. in the UK Electrical Forum area at ElectriciansForums.net
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...