Hi, I have been out to a property 3 times in the past week to a country pile with a 3 phase supply that keeps blowing it's 100amp distributor fuse.

The property has a pool house, a large garage with power, stables with power and a wooden annex type space also with power.

I have taken off every accessory in this huge place and can't find any obvious issues.

At the board I have measured a PFC of 1.19 kA and a PSCC of similar.

Nothing trips in the board when the dist fuse goes, I've not done a lot of work with 3 phase so unsure where to go from here.

Any advice much appreciated.
 
Sit down with the customer, try to analyze the situation,
Try to establish a pattern to it,
When does it blow ? What time of day or night ?
What is likely in use ? What was recently turned on ?
Don't forget automatically controlled loads too,
Like pumps and water heaters.
 
It is unlikely that any accessory is causing a main fuse to blow, more likely to be an overload. Has anything been added recently?
They say not but then having said that I found a whole floor via the loft they hadn't even mentioned to me! Everything is in old colours except for 2 circuits, 1 of which is lighting and the other I'm not sure at this stage as it's not labeled, hence one of the reasons for looking at all accessories.
 
Evidently otherwise I wouldn't have been able to post the PFC and pssc. Do you have anything constructive to add such as the logical approach you would take?

The logical approach of take is to think about what might cause a cutout fuse to blow without any mcb operating.
So either a fault between the cutout and the DB, am overload, or loose connections/overheating of the cutout.
Therefore randomly removing accessories is a waste of time and the customers money.

Why measure the PFC and PSCC? Did you carry out any other tests?
 
Taken off all accessories in a place like that ? That would take me a week I reckon. Wouldn't even consider that in the event of a phase loss.

Overload would be my first thought at that place and I would check the load balancing and take some measurements.

What bearing do old coloured cables have on this ?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Leicester, UK

Thread Information

Title
3 phase domestic installation issues
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
51
Unsolved
--

Advert

Thread statistics

Created
Karl Atkins,
Last reply from
delano,
Replies
51
Views
9,653

Advert

Back
Top