lurch

-
Joined
Feb 5, 2009
Messages
276
Reaction score
43
Some advice please. . . I have a local community centre (old prefab) that has a 3 phase TNS supply from the local DNO. I have carried out a EICR which has unsatisfactory on various points, however I am trying to locate the regulation that covers isolation. . . . the scenario is 3 phases in to 3 phase meter, and then 3 separate single phase domestic Consumer units, all located within a cupboard.

My concern is that there is no single point of isolation on the 3 phase supply. I want to give this a C2 but not having come across this scenario before and want to know the regulation that covers this . . . if there is one. Or is it totally acceptable to have this setup as it is. . . . constructive answers always welcome.
 
Some advice please. . . I have a local community centre (old prefab) that has a 3 phase TNS supply from the local DNO. I have carried out a EICR which has unsatisfactory on various points, however I am trying to locate the regulation that covers isolation. . . . the scenario is 3 phases in to 3 phase meter, and then 3 separate single phase domestic Consumer units, all located within a cupboard.

My concern is that there is no single point of isolation on the 3 phase supply. I want to give this a C2 but not having come across this scenario before and want to know the regulation that covers this . . . if there is one. Or is it totally acceptable to have this setup as it is. . . . constructive answers always welcome.
You have 3 points of isolation 1 on each Consumers Unit.
 
see pic for info

[ElectriciansForums.net] 3 phase supply, advice required
 
agreed. . . but Ive always had it drummed into me from way back that there should be a single point of isolation in the event of an emergency
You would be extremely unlucky to have an emergency on all SP&N CUs at once Lurch, think the isolation matter is covered. Remember it may be a 3 phase supply, but all you have is 3 SP&N Systems
 
Last edited:
Some advice please. . . I have a local community centre (old prefab) that has a 3 phase TNS supply from the local DNO. I have carried out a EICR which has unsatisfactory on various points, however I am trying to locate the regulation that covers isolation. . . . the scenario is 3 phases in to 3 phase meter, and then 3 separate single phase domestic Consumer units, all located within a cupboard.

My concern is that there is no single point of isolation on the 3 phase supply. I want to give this a C2 but not having come across this scenario before and want to know the regulation that covers this . . . if there is one. Or is it totally acceptable to have this setup as it is. . . . constructive answers always welcome.
If it was my job, i would fit a 4 pole 100a isolator, much the same as your electrical utilities supplier would fit. Not expensive, and sorts out the "one point of isolation" reg. Hope this helps.
 
You would be extremely unlucky to have an emergency on all SP&N CUs at once Lurch, think the isolation matter is covered. Remember it may be a 3 phase supply, but all you have is 3 SP&N Systems
agreed. . . but all it takes is for joe public to look in cupboard and isolate wrong board. . . I like to make life simple for 'em. Furthermore, if boards were sited in 3 separate locations I get it, but if I were to do this job from scratch it would be a TPN bioard end of . . . . but that's not the case.
 
If it was my job, i would fit a 4 pole 100a isolator, much the same as your electrical utilities supplier would fit. Not expensive, and sorts out the "one point of isolation" reg. Hope this helps.
Not a bad idea Steve, but if you relyon the Isolator you mention as the single point of isolation, problem occurs in one particular SP system, then you would isolate all three CUs. Just a thought.
 
You would be extremely unlucky to have an emergency on all SP&N CUs at once Lurch, think the isolation matter is covered. Remember it may be a 3 phase supply, but all you have is 3 SP&N Systems
Hi Pete, I don't think it makes any difference whether its a 3 phase supply or a single phase!
A local plumber in Prestwich,Manchester turned off the consumer unit, because he was going to change the shower. What he didn't spot was a Wylex 104 in the corner of the mains cupboard. Consequently, the world is one plumber less.
 
Hi Pete, I don't think it makes any difference whether its a 3 phase supply or a single phase!
A local plumber in Prestwich,Manchester turned off the comsumer unit, because he was going to change the shower. What he didn't spot was a Wylex 104 in the corner of the mains cupboard. Consequently, the world is one pluber less.
Could happen anywhere switching off the wrong Mains Switch, just an important question, was the Plumber trained in the Safe Isolation Procedure? seems not in this
instance.
 
Hi Pete, I don't think it makes any difference whether its a 3 phase supply or a single phase!
A local plumber in Prestwich,Manchester turned off the consumer unit, because he was going to change the shower. What he didn't spot was a Wylex 104 in the corner of the mains cupboard. Consequently, the world is one plumber less.
this highlights the point I am making. . . if there was a single point of isolation then this wouldn't of happened. we are obsessed in this country on cutting into meter tails and hooking in additional cu's .
 
Hi Pete, I don't think it makes any difference whether its a 3 phase supply or a single phase!
A local plumber in Prestwich,Manchester turned off the consumer unit, because he was going to change the shower. What he didn't spot was a Wylex 104 in the corner of the mains cupboard. Consequently, the world is one plumber less.
As Pete mentioned he obviously didn’t follow the correct procedures, a simple voltage tester would of saved him yet he got complacent.
 
Hi Pete, I don't think it makes any difference whether its a 3 phase supply or a single phase!
A local plumber in Prestwich,Manchester turned off the consumer unit, because he was going to change the shower. What he didn't spot was a Wylex 104 in the corner of the mains cupboard. Consequently, the world is one plumber less.
As Pete mentioned he obviously didn’t follow the correct procedures, a simple voltage tester would of saved him yet he got complacent.
 
Each consumer unit has a means of isolation to their respective circuits.
I can’t see how not having a single point of isolation may result in potential danger to the user of the installation of anyone else.
 
clearly not.
Now we are moving into the realms of assuming that everyone is foolproof, just because they are a tradesman. Today's "super regs" have been drawn up, assuming that everyone that's not electrically qualified is a moron. The incident i brought up happened in the days before thins like RCDs MCBs etc, but a single point of isolation would have saved his life.
 

Reply to 3 phase supply, advice required in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
498
  • Question
Three phase or single phase it is not correct.
Replies
1
Views
494
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
289
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
670
  • Question
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks