Some advice please. . . I have a local community centre (old prefab) that has a 3 phase TNS supply from the local DNO. I have carried out a EICR which has unsatisfactory on various points, however I am trying to locate the regulation that covers isolation. . . . the scenario is 3 phases in to 3 phase meter, and then 3 separate single phase domestic Consumer units, all located within a cupboard.

My concern is that there is no single point of isolation on the 3 phase supply. I want to give this a C2 but not having come across this scenario before and want to know the regulation that covers this . . . if there is one. Or is it totally acceptable to have this setup as it is. . . . constructive answers always welcome.
 
Since when is it any business of the NICEIC what the regs state? Its either compliant or its not, yet they make a comment that neither confirms it or isnt. Yet people still fall over themselves for these scams.
Am not a QS so was not present during the inspection, this was just feed back from my supervisor.
It’s always stuck in the back of my mind tho.
 
Each consumer unit has a means of isolation to their respective circuits.
I can’t see how not having a single point of isolation may result in potential danger to the user of the installation of anyone else.
. . . picture this scenario. Fault on circuit 1 on DB 1. "quick isolate that circuit Dave!" Dave goes to cupboard and isolates first main switch he sees. "Done" . . . but is it??
 
I would not hesitate in asking a customer who has rung me to report a smell of burning to go to mains and isolate a main switch until I can get there. This is hardly messing with a board !!!

But if they don't know what they are doing and which board to isolate then maybe you should be telling them to isolate all 3.
 
I would not hesitate in asking a customer who has rung me to report a smell of burning to go to mains and isolate a main switch until I can get there. This is hardly messing with a board !!!
What's wrong with the Main Switch on the Consumers Unit? Not messing with a Board? but you will be messing with other peoples supply of electricity wouldn't you??
 
Exactam
I would be asking why “Dave” didn’t ask which board in this instance.
Exactamundo, Dave goes to the Cupboard, switches OFF the TP&N isolator, Mrs Brown in the flat in question knows the juice is going OFF Mrs Smith and Mrs Jones in the other two flats call out an Electrician to find out the problem, because their Electric is no more, ergo confusion rules OK?
 

Reply to 3 phase supply, advice required in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
969
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
388
I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top