What local distribution network, all of these things can be found on a small domestic install these days, I'm not going to back down and no one has yet given proof that the N cannot be overloaded in the scenario given by the OP.
So until this is done I stand by my arguments, I DESIGN, I DO NOT GUESS values, so the N can be overloaded, & if I was being paid for my consultancy then I would be bothered to calculate things, as I am not, it;s down to you lot to prove otherwise, which, as yet, you have failed to do.
Fantastic thread guys.............well done to all.
Great stuff![]()
Hahaha...must have a proper read tomorrow!
The original Q just appears to be an unbalanced Star with a Neutral, what's the problem?!?! :sifone::smilielol5:
In the OP, the N conductor CAN be overloaded.
The circuit is not acceptable.
If anyone can PROVE otherwise in all scenarios then I will bow down, until then I await proof.
Point 1: I still maintain that the circuit can be overloaded on the N conductor, as no-one has proven otherwise with 3 off socket outlet circuits as the point of use.
Point 2: I'm not talking about PF, here either, we are at least talking harmonics & distorted N currents, which you cannot ignore.
Whilst the simplification I posted earlier I agree may have been a little "too" simple at 60A due to the 3 x 20A phase currents, no one has proven as yet that this cannot happen, & I don't believe that anyone can, when the final loads are unknown!
I'm not convinced & I still stand by the fact that the N currents can sum, and no one yet has proven otherwise, it is actually easy to prove they can, but I'm not here to do that.
OK, sorry missed the one per phase bit, read it as one per socket!
So currents will be reduced as per load reduction, the loads are now perfectly balanced (within reason) so the current drawn per phase will be say for arguments sake 13A
Harmonics have got all the DNO's very worried these days, and for very good reason too!! Those 3 1/2 core cables they installed just about everywhere, are coming back to bite them in the arse!! Not quite the money saving solution they once thought them to be!! lol!!