OK,
I can see where those of you who say that the N current will be delayed by 120 degrees, this would be the case with balanced 3 phase loads of known characteristics.
It cannot be guaranteed to be the case with 3 off single phase socket outlet circuits spread across 3 phases, you have no control over what the loads are or what they an "do" to the N return current, you cannot assume that the N return current will be phase balanced.
There are too many non-linear loads in current installs.
If the loads are perfectly balanced then why do we not use 1/2 size N conductors for 3ph boards all the time now?
 
Forget balancing, it is completely irrelevant to this discussion.

Even still, take a TP+N load, L1 = 100A, L2 = 0A, L3 = 0A then N = 100A.

The neutral current can never exceed the line current!

If you can guarantee a specific Ib to stay at a certain value per phase then it is completely permitted to calculate the size of the neutral conductor required and install that.
 
It doesn't matter, the L current per phase will be out of phase with the others, and so will the neutral current.

Bad design for sure, but absolutely no danger.
 
Yes it could be out of phase, but by how much, and, why are all 3 phases bound to be loaded at the same time and by the same amount and with a suitable phase shift to ensure that the N cannot be overloaded, you cannot guarantee that they will, you can get sufficient phase shift to overload the N, remember there are so many non-linear loads around now and the OP does not define what is connected.
There are too many unknowns to give this an OK.
 
You're not going to get any plug in non-linear loads without suitable PF correction fitted within. Even still, any negative effects caused by slight inductance or capacitance will be negligable.
 
You're not going to get any plug in non-linear loads without suitable PF correction fitted within. Even still, any negative effects caused by slight inductance or capacitance will be negligable.

I can understand where Paul is coming from, with a purely theoretical view, but as a practical application I have to go with this ^^^ ..... We're talking about some sockets in a dado trunk, not industrial connections.
 
So you are categorically stating that if 2 off 20A single phase loads were plugged into 2 separate single phase circuits they could NEVER overload the 2.5mm sq N conductor?

No, I'm just saying it's HIGHLY improbable.

Think of TP+N lighting power track systems. These share a common neutral and are protected by TP OCPDs. Commonly these are also fluorescent fittings, an assumption can be made that a standard rate of cap faliure within the fittings will equal itself out over time across the three phases thus causing very little cause for concern. Still, installations like these need regular maintenance where things like this SHOULD be picked up if the guys are doing their job properly.

Like I said, the circuit brought to discussion in the OP is badly designed with it's use in mind, however it would cause me no concern if I came across the same thing on an install.
 
Thing is you don't know what is going to be plugged in.

Not sure what I'll be having for breakfast, either! You can over-think things sometimes.
 
Stuff lighting! ;)

Have you ever analysed the non-linearity of power loads in even a simple domestic install these days?

Think SMPSU's, your fluoro fittings, motor loads, vsd's in washing machines, yes, there will be pfc, & each should individually meet the requirements of the LVD & the EMCD, but cumulatively this can have a significant affect on the connected systems, so i stand by my points that the loads can sum as they can be way out of phase.
Take an accurate power analyser and check a few installs and see what you get at the tails, then guarantee me that you can never overload the N in this scenario.
 

Reply to 3 sp circuits off a tp isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
223
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
837
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
830

Similar threads

If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top