Can any one tell me if i need to put rcd on 3036 cu if I am just changing socket faces cause i was told i did?
Last edited by a moderator:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3036 with RCD in the Australia area at ElectriciansForums.net
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).
not that its important for this post but i thought a 1361 was 33Ka
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).
not that its important for this post but i thought a 1361 was 33Ka
It is 33kA but the BS60439-3 UK annex only allows us to allow 16kA when used for this purpose.
The discolouring on the second white fuse carrier looks like 'flash' to me, from where a BS3036 has 'blown' on a fault.
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).
not that its important for this post but i thought a 1361 was 33Ka
1361 type 2 is 33ka 1361 type 1 is 16.5 ka
looking at the pics though the discolouration of the fuse carrier is due to the fuse blowing and not to overload , meter tails look like 16 mm ,and if im not mistaken the fuse carrier is a 3036 rewireable , if i am mistaken and i could be then the fuse may will be a BS88 or a 1361 , think ive mentioned them all , but id be suprised if the fuse was any higher than a 60 amp , have a close look at the fuse carrier it may well give you the fuse rating (capacity) on it
anyone else confirm 4ka is the rating for 3036 fuses?
if not and its 1ka for the 5a lighting for example does it not matter that my PFC is greater than this cappacity?