Can any one tell me if i need to put rcd on 3036 cu if I am just changing socket faces cause i was told i did?
 
Last edited by a moderator:
im asking due to a PIR on this install.

cant identify the cut out rating and the tails look very small, from the cutout to the meter is 16mm, out the meter to CU looks smaller to me, poss 10mm..

also signs of overloading on lights, (cant see how though, only 5 pendants on the circuit)

and broken fuse carrier
and no cover on the front for the fuses
 

Attachments

  • IMG_1398.jpg
    IMG_1398.jpg
    144.5 KB · Views: 69
  • IMG_1397.jpg
    IMG_1397.jpg
    188.4 KB · Views: 67
I can't comment on the tails size from a photo.

The discolouring on the second white fuse carrier looks like 'flash' to me, from where a BS3036 has 'blown' on a fault.

They don't make 'em like that any more (thank god).
 
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).
not that its important for this post but i thought a 1361 was 33Ka

It is 33kA but the BS60439-3 UK annex only allows us to allow 16kA when used for this purpose.
 
The discolouring on the second white fuse carrier looks like 'flash' to me, from where a BS3036 has 'blown' on a fault.

That was my first thought but then noticed the customer had put 15a fuse wire in to replace the 5.

the tails had been doubled back in the terminals which is why i thought they were 10mm. could be one of the old dodgy size conductors.
 
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).
not that its important for this post but i thought a 1361 was 33Ka

1361 type 2 is 33ka 1361 type 1 is 16.5 ka

looking at the pics though the discolouration of the fuse carrier is due to the fuse blowing and not to overload , meter tails look like 16 mm ,and if im not mistaken the fuse carrier is a 3036 rewireable , if i am mistaken and i could be then the fuse may will be a BS88 or a 1361 , think ive mentioned them all , but id be suprised if the fuse was any higher than a 60 amp , have a close look at the fuse carrier it may well give you the fuse rating (capacity) on it
 
lenny looking at it somethings not right you can see a black identified with blue tape and a neutral on the L/H of the neutral bar , but why has the black been marked with brown tape is it 2 blacks im confused ????? 3 blacks 1 red !!
 
It does look odd at first glance.

Looking into it shows the shower circuit is wired via 6.0mm 4 core stranded flex, not sure what the cable BS number is, has a thick grey outer insulation, copper strands.

This is why they are all black but have been taped up to identify conductors.

No markings on the fuse carrier as to what size or type. im guessing BS88 because of its shape/length
 

Reply to 3036 with RCD in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
245
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD...
Replies
9
Views
1K
nicebutdim
N
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
611

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top