Can any one tell me if i need to put rcd on 3036 cu if I am just changing socket faces cause i was told i did?
 
Last edited by a moderator:
Yep seen that, heard you loud and clear..

But i dont think i have a 1361 main fuse..

and i always see this ka rating 1 to 4 on 3036 fuses but which is it... 1,2,3 or 4?

Have a careful look on the fuse holder and you might just be lucky and see S1A, or S2A on it. 1 means a breaking capacity of 1kA and 2 is for a BC of 2kA. unfortunately a lot of them have nothing but dead spiders in them!

If you have a type 1 bs1361 main fuse you can use its BC of 16.5kA (type 2 is 33kA) , but if it is a BS 88-6 their BC is also 16.5kA :)

If you come across the old bs 3871 circuit breakers it is the "M" number on the side that tells you the BC eg M3 is a BC of 3kA.


edit ; should have said that you can only rely on the upstram fuse if the CU is to BS 5486-13 or BSEN60439-3 and with your missing cover if it was to the BS standard it won't be now. :(

However in this http://www.esc.org.uk/pdfs/business-and-community/SwitchedOn-Issue-17.pdf from the ESC (page18?) it says that the BC of 3036s in domestic use was the 2kA versions . Which would mean with your pfc you are ok :)
 
Last edited by a moderator:
Do cables buried at less than 50mm on a PIR mean an RCD should be present. Not sure it does. Otherwise 90 % of DBs in UK would need replacing. Sockets should always have an RCD but lack of them on a PIR does not constitute a code 1 unless external sockets lack RCD protection.
 
Do cables buried at less than 50mm on a PIR mean an RCD should be present. Not sure it does. Otherwise 90 % of DBs in UK would need replacing. Sockets should always have an RCD but lack of them on a PIR does not constitute a code 1 unless external sockets lack RCD protection.

Dolph, do you have a 17th edition qualification?

Cables buried at depths of less than 50mm without earthed metallic sheaths etc. should always be a code 4 on a PIR!

Of course the DB would not need to be replaced!

Lack of rcd protection to sockets not expected to supply equipment outdoors would be a code 4 and a code 2 if outdoor equipment was expected to be supplied.

It is really important to get basic regulation information right before posting advice.

Have a read of this: http://www.esc.org.uk/pdfs/business-and-community/electrical-industry/BPG4_08.pdf it should be of some assistance.
 
Think we may have wires crossed, I was simply stating that a DB would would not need replacing with the 50mm reg etc etc. You'd be surprised how many sparkys think it does!


Yes I do have a 17th ed qualification, but thanks for the link anyway.

Codes regarding socket outlets will be altering next year when the new EICR will be launched replacing PIRs. But that's for another day I guess.

And as regards correct info is'nt that the point of a forum. To learn and share ideas?


By the way my latest film 'The Expendables' is out 2 weeks today on DVD and Blu - Ray.
 

Reply to 3036 with RCD in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
245
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD...
Replies
9
Views
1K
nicebutdim
N
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
611

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top