I had a case in the spring. On carrying out R1+R2 tests there was no cpc continuity at the metal kitchen light fitting, although the owner had connected the cpc when he put the fitting up.
Couldn't access the space between the kitchen and bathroom above due to glued laminate flooring in the bathroom, so had to cut a hole in the kitchen ceiling, hoping to find where the problem was.
Here's what I found, thanks to someone who thought JB's under floorboards were a good idea...
Couldn't access the space between the kitchen and bathroom above due to glued laminate flooring in the bathroom, so had to cut a hole in the kitchen ceiling, hoping to find where the problem was.
Here's what I found, thanks to someone who thought JB's under floorboards were a good idea...