Afternoon all,

Looking for a little guidance, other than doing sub mains in armoured I don’t do much three phase work.

I’m looking to install some final
Circuits for some three phase cooking equipment but I find myself stuck on a few things, as the sockets will be over 16amp they will need to be rcd protected but I can’t seem to find anything to find a Hager board rcbo etc. What’s the best way to protect it?

Also generally if doing a three phase sub main I would take an additional earth as I’m not so keen on solely relying on the armoured earth. Do most people generally rely on the armoured earth or use 5core?

Thanks for your help
 
I’m not disputing the need for a plug and socket only the need for RCD protection..
Up until now equipment in this environment hasn’t needed to be considered for RCD protection..

Over the years there have been many things which have changed in the regulations resulting in this same type of situation. Something now needs to be done differently to how it used to be done, why not accept the change as a chance to improve safety rather than fighting against it?

People reacted the same way when RCDs became a requirement for all general purpose socket outlets regardless of whether they could be used outside or not, now everyone just accepts it as the norm. In a couple of years time the general consensus will change and this situation will be accepted as the norm.
 
The purpose of A Risk Assessment is to identify potential risks and hazards. Then put in place measures to minimise each of the risk’s.

In this case we would have to identifying if there is a risks of HAVING the RCD in circuit in order for there to be a risk reduction in omitting the RCD.
 
Why are people so dead set against having RCD protection fitted to these socket outlets?

There are very specific circumstances where the 30ma RCD can cause genuine problems. One i deal with regularly is sockets to supply temporary electrical distribution for entertainment ie sound and lighting for festivals. The overall earth leakage of the connected equipment can add up fast without being near 32amp load. These sockets generally connect to portable power distribution that has individual rcbo’s on each circuit. The original proposal to rase the requirements for rcd’s to 63amp where thankfully dropped.

But this is way off topic. Apologies.
 
There are very specific circumstances where the 30ma RCD can cause genuine problems. One i deal with regularly is sockets to supply temporary electrical distribution for entertainment ie sound and lighting for festivals. The overall earth leakage of the connected equipment can add up fast without being near 32amp load. These sockets generally connect to portable power distribution that has individual rcbo’s on each circuit. The original proposal to rase the requirements for rcd’s to 63amp where thankfully dropped.

But this is way off topic. Apologies.

I work in the same area, theatre and outdoor events. 30mA RCDs don't cause problems, the inappropriate use of them causes the problems.

I can't say I've ever had a problem providing 30mA RCD protection to final circuits.
Problems only happen when people do stupid things like putting distribution circuits on 30mA RCD.
 
I work in the same area, theatre and outdoor events. 30mA RCDs don't cause problems, the inappropriate use of them causes the problems.

I can't say I've ever had a problem providing 30mA RCD protection to final circuits.
Problems only happen when people do stupid things like putting distribution circuits on 30mA RCD.

Yes exactly. Im talking about the supply socket for the distribution to connect to.
 
Simple really. Either fit an RCD or the designer conducts a risk assessment, bearing in mind they will have to justify their decision that RCD protection was not necessary, possibly in a court of law, especially if someone was killed or injured as a result of the RCD protection being omitted.
 
Why are people so dead set against having RCD protection fitted to these socket outlets?

Not dead against. Just accepting that they are not always required and are not always necessary.

For example we install 32A TP+N sockets for retail kiosks on stations. We do not install these on RCDs as they will ultimately be distribution circuits so our risk assessment will insist that the kiosk will have all circuits independently protected by RCDs.
 
Not dead against. Just accepting that they are not always required and are not always necessary.

For example we install 32A TP+N sockets for retail kiosks on stations. We do not install these on RCDs as they will ultimately be distribution circuits so our risk assessment will insist that the kiosk will have all circuits independently protected by RCDs.
Are you telling us that you get such RAs accepted by National Rail and TFL?
 

Reply to the thread, titled "415v 3 phase sockets and rcd protection." which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top