has anyone spured off a 4mm radial in 2.5mm on 75 mtrs circuit length on 32A mcb
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 4mm radial in the UK Electrical Forum area at ElectriciansForums.net
Doesn't really matter as it should be protected by an RCD anyway!
Answer appendix 15
Doesn't really matter as it should be protected by an RCD anyway!
To spur off in 2.5mm feeding a max. of 1 x 13A Twin socket, although unconventional, is technically ok. The reason why this is ok is the max. amount of current that can be drawn by this twin socket is 13A (Well that is what they are designed to take, not 13+13 = 26A. Sockets, single or twin are designed to take 13A total).
2.5mm is rated max at 27A (clipped direct or in plaster) - Due to the plug top fuse being 'down stream' this limits the amount of current that can be drawn.
The 2.5mm is protected by fault current by the 32A MCB, this is where the adiabatic equation comes into platy to prove this. (However, we should already know that it is ok to spur off a 32A ring circuit with 2.5 to feed one point).
Fuse doesn't always have to be at origin. Downstream protection is common. Think Busbar chambers and meter tails....
I was under the understanding that the max drawable from a 2G socket under normal domestic conditions was 26A? i.e. 2x 13A plug tops (with three 4G ext leads running of them).
When did this change, i cant see any difference now than 5 or 10 years ago years ago.