has anyone spured off a 4mm radial in 2.5mm on 75 mtrs circuit length on 32A mcb
 
To spur off in 2.5mm feeding a max. of 1 x 13A Twin socket, although unconventional, is technically ok. The reason why this is ok is the max. amount of current that can be drawn by this twin socket is 13A (Well that is what they are designed to take, not 13+13 = 26A. Sockets, single or twin are designed to take 13A total).

2.5mm is rated max at 27A (clipped direct or in plaster) - Due to the plug top fuse being 'down stream' this limits the amount of current that can be drawn.

The 2.5mm is protected by fault current by the 32A MCB, this is where the adiabatic equation comes into platy to prove this. (However, we should already know that it is ok to spur off a 32A ring circuit with 2.5 to feed one point).

Fuse doesn't always have to be at origin. Downstream protection is common. Think Busbar chambers and meter tails....
 
In real terms, I don't see the point of changing to 2.5 just for one 'spur'. Why not just use 4mm like the rest of the circuit? It is then just a branch off the radial, and also leaves the option of adding onto the end in the future.
 
To spur off in 2.5mm feeding a max. of 1 x 13A Twin socket, although unconventional, is technically ok. The reason why this is ok is the max. amount of current that can be drawn by this twin socket is 13A (Well that is what they are designed to take, not 13+13 = 26A. Sockets, single or twin are designed to take 13A total).

2.5mm is rated max at 27A (clipped direct or in plaster) - Due to the plug top fuse being 'down stream' this limits the amount of current that can be drawn.

The 2.5mm is protected by fault current by the 32A MCB, this is where the adiabatic equation comes into platy to prove this. (However, we should already know that it is ok to spur off a 32A ring circuit with 2.5 to feed one point).

Fuse doesn't always have to be at origin. Downstream protection is common. Think Busbar chambers and meter tails....

Eh? lost me there unswitched.
 
I was under the understanding that the max drawable from a 2G socket under normal domestic conditions was 26A? i.e. 2x 13A plug tops (with three 4G ext leads running of them).
 
I was under the understanding that the max drawable from a 2G socket under normal domestic conditions was 26A? i.e. 2x 13A plug tops (with three 4G ext leads running of them).

Two gang sockets seem like a bit of a grey area to me. Nothing to stop someone drawing 26A through one yet most have 13A stamped on them but are actually rated up to 20A (?)....I always feel better using a decent quality socket like an MK or Contactum. I also find these will take 2 x 4mm quite easily. My dad gave me a big box of old but unused Contactum accessories, nearly used them up now, but they have been a joy to work with.
 
Your MK link doesnt work TC.
Anyways my 2p is that you'll never get 3 4mm wires in a standard socket terminal anyway.
And most BS double sockets are rated at least 20A.
 
Last edited by a moderator:

Reply to 4mm radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
414
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top