has anyone spured off a 4mm radial in 2.5mm on 75 mtrs circuit length on 32A mcb
 
Just goes to show the variability of assessors, I know someone in ECA/Elecsa who continually preaches the Zs = Ze + R1 + R2 calculation and EIC entry
I personally don't like calculated Zs on an EICR unless I really have to. I doesn't give you a true picture of what is happening with that specific circuit within an installation, parallel paths etc.
 
I personally don't like calculated Zs on an EICR unless I really have to. I doesn't give you a true picture of what is happening with that specific circuit within an installation, parallel paths etc.

No, but that is the point.

You need to ensure that the opd will operate if the parallel paths are removed in the future.

As I said, I do not consider a measured Ze (without parallel paths) and a measured R1+R2 to be what is meant by a 'calculation'.
 
Geoff, I see your point. We could debate this until the bovines come home. :lol:

There are valid reasons for both methods, otherwise they wouldn't be accepted as test methods. In a domestic installation there is little likelihood of circuits being removed but in industrial and commercial there is. I think it would be down to the tester at the time to make an informed decision as to what method to use and even both if the need arises or is requested.
 
Last edited:
It has gone off topic a bit...

Dependant upon intended use, load, CCC and voltage drop .

BGB is in the van but BRB page 363 Fig 15.

Unfused Spur on a 30A or 32A ocpd.

An unfused spur run in 2.5mm2 cable should feed one single or one twin socket outlet only. An unfused spur may be connected to the origin of the circuit in the distribution board.

It all boils down to voltage drop and what the intended load is.
 

Reply to 4mm radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
414
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top