has anyone spured off a 4mm radial in 2.5mm on 75 mtrs circuit length on 32A mcb
I personally don't like calculated Zs on an EICR unless I really have to. I doesn't give you a true picture of what is happening with that specific circuit within an installation, parallel paths etc.Just goes to show the variability of assessors, I know someone in ECA/Elecsa who continually preaches the Zs = Ze + R1 + R2 calculation and EIC entry
I personally don't like calculated Zs on an EICR unless I really have to. I doesn't give you a true picture of what is happening with that specific circuit within an installation, parallel paths etc.
I haven't.has anyone spured off a 4mm radial in 2.5mm on 75 mtrs circuit length on 32A mcb
It all boils down to voltage drop and what the intended load is.Unfused Spur on a 30A or 32A ocpd.
An unfused spur run in 2.5mm2 cable should feed one single or one twin socket outlet only. An unfused spur may be connected to the origin of the circuit in the distribution board.