sedgy34
has anyone spured off a 4mm radial in 2.5mm on 75 mtrs circuit length on 32A mcb
Your MK link doesnt work TC.
Anyways my 2p is that you'll never get 3 4mm wires in a standard socket terminal anyway.
And most BS double sockets are rated at least 20A.
that's why 4mm is stranded. so you can snip a few off to make them fit. only joking, before i'm crucified)
Of course you can.Anyways my 2p is that you'll never get 3 4mm wires in a standard socket terminal anyway.
Of course you can.
How much thicker do you think it is?
Hi biff it worked yesterday but not today so i will try it again.
If it does not work go to MK site, wiring devices and downloads.
http://www.mkelectric.com/Documents/English/EN%20MK%20Technical%20Specifications/T02%20LOGIC%20PLUS%20Tech%20355-389.pdf
Read it and weep. Lol
This is allowed page 363 IEE Wiring Regs 17th Edition. Hope this settles it
Something i am confused over with Zs is if the circuit is protected by an RCD, as is the case for 90% on a 17th edition board (and the tripping times are within limits) could you put "N/A" in the box for "max measured earth fault loop impedance?Doesn't really matter as it should be protected by an RCD anyway!
You need the still confirm Zs is a reasonable value, based on Zs = Ze + R1 + R2. If using software package to fill in results then to stop the software complaining the measurent is out of spec you should be able to put in max allowed Zs as 1667.
I was told off by my NIC inspector for putting down Zs = Ze + R1 + R2 as calculated not measured (i had put down on EIC a note to say that it was a calculation).
He said why do you do it that way? I said because the last inspector told me to!
Well i am telling you to do it by measurement.
I asked is there anything technically wrong in doing it by calculation?
He mumbled no under his breath (as long as you make a note on the EIC) but still wants it done by measurement!
What do most of you do?
I queried this at my last ELECSA assessment, particularly regarding the more awkward circuits to test. The assessor said that I should be doing a live Zs test on all circuits. He said that live testing was part of the job and not the same as live working.