usually want you to put a KMF (with an 80A fuse) in if the tails are over 2 or 3 metres long. for some reason.
The reason is that the DNO are quite happy for you not to fit a protection device after the meter on your tails, as there fuse will afford it protection. Anything over 3-5 mteres depending on the DNO, they will not provide that protection and so you need to fit a protection device, normally a BS 1361 fuse.