For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.

It was published in 2005 but the important bits remain unchanged and might be of some help!
 

Attachments

  • Garage-Shed Supplies.pdf
    243.4 KB · Views: 6,062
This really needs to go back in the ''Sticky section'' above!! It seems that there are still far too many here, that have been brainwashed by the scaremongers into believing you can't extend a PME equipotential zone, or take a PME CPC with you to an outbuilding or shed!!
 
Hi, great thread - quick question... I'm installing power and light to a workroom in the back of a detached barn. Supply is off a spare way in the house and will feed a small consumer unit in the barn. The barn cu will have 30ma RCDs so my question is: Am I right to use a 100ma RCBO at the house so the whole thing doesn't automatically trip?
 
Hi, great thread - quick question... I'm installing power and light to a workroom in the back of a detached barn. Supply is off a spare way in the house and will feed a small consumer unit in the barn. The barn cu will have 30ma RCDs so my question is: Am I right to use a 100ma RCBO at the house so the whole thing doesn't automatically trip?

Also, there is a strong possibility that the 100mA at the house will trip at the same time as to 30mA in the barn. You will need a time-delayed (s-type) RCD in the house if you want to provide discrimination whilst protecting the supply cable. Not sure whether you are an electrician or not, so just to let you know, this job would be notifiable to your LBC.
 
As Guitarist said, the 100mA device will almost certainly trip simultaneously with a 30mA device downstream-does this 'supply cable' actually REQUIRE RCD protection?
 
Ah, just noticed all the other replies, sorry guys, my first time here. Yes I am an electrician, qualified 2yrs ago but this job isn't my usual bag. Yes the cable does require RCD protection as it will be supplying power for outdoor use. The installation in the barn is entirely fitted in conduit.
 
Ah, just noticed all the other replies, sorry guys, my first time here. Yes I am an electrician, qualified 2yrs ago but this job isn't my usual bag. Yes the cable does require RCD protection as it will be supplying power for outdoor use. The installation in the barn is entirely fitted in conduit.

That in itself is not a requirement for RCD protection of a distribution circuit.
 

Reply to A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top