For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.

It was published in 2005 but the important bits remain unchanged and might be of some help!
 

Attachments

  • Garage-Shed Supplies.pdf
    243.4 KB · Views: 6,062
Thanks, but some of us have been taught that the DNO will not accept that on a TNC-S system. I am not trying to be contentious here but wonder where that myth came from.

From bias lectures that don't like PME earthing!! That seems to be one of the biggest influences anyway!! Same goes for RFC's, Using the Armour of SWA cables as the circuits CPC, and a few others too boot as well...lol!!
 
What another cracking thread. So in summary so I can go forward,

1) We can export if practicable, if not TT it with all the usual requirements.

2)If we do export then a 10mm Main bonding cable must be provided, if services enter the location

3) If the CSA of the supply cable is <10mm we must provide a separate Main bonding conductor of 10mm

4)If the supply cable CPC CSA is > 10mm or + we can use said CPC as our 10mm main bond


Have I missed anything ?

My understanding from gn8 IS your exported bonding coductor size is the same as you bonding conductors for your main installation so if your main bonding is 50mm then your bonding to your outbuilding/shed will be 50mm even if your supply conductor size is only 16mm(to the out building)
 
I have GN8 on back order from Amazon can't wait to get my nose in it..sad ain't i....
The was a time I would have a crumpled copy of Mayfair or Penthouse rammed down the back of the toilet systen..now it's electrical pawn lmao

ATB J
 
My understanding from gn8 IS your exported bonding coductor size is the same as you bonding conductors for your main installation so if your main bonding is 50mm then your bonding to your outbuilding/shed will be 50mm even if your supply conductor size is only 16mm(to the out building)

Yes, the main protective bonding conductors on a PME system are sized in accordance with the SUPPLIERS neutral conductor (not the tails) and as you rightly say, there is no provision to reduce the size in a distribution circuit to another building with main protective bonding requirements.
 
I'm just bumping some of the older threads in the general electrical forum that had a lot of replies. They might not be current topics, if they're not, just ignore them and they'll soon drop off the list. If you DO wish to add a reply and get the conversation going again, feel free to do so. Your input might help somebody else in the future.
 

Reply to A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top