For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.

It was published in 2005 but the important bits remain unchanged and might be of some help!
 

Attachments

  • Garage-Shed Supplies.pdf
    243.4 KB · Views: 6,178
Please excuse a newbie butting in to this fascinating exchange of views.

I read somewhere years ago that the main reason why it is good practice to bond the reinforcing matting in concrete floors in livestock buildings is that cows are extraordinarily sensitive to potential differences through their feet.

I’m not making this up!

It can apparently be difficult to drive stock into a building across the PD that could be created by an unbonded floor. This could be a long-forgotten reason why livestock buildings are selected for special treatment in guidance notes.

Farmers have apparently blamed supernatural influences at work, when the real reason was a volt or two between a building’s floor and the ground outside

Otherwise what’s so special about ‘livestock’ buildings? Don’t forget that most houses are occupied by primates.
 
Please excuse a newbie butting in to this fascinating exchange of views.

I read somewhere years ago that the main reason why it is good practice to bond the reinforcing matting in concrete floors in livestock buildings is that cows are extraordinarily sensitive to potential differences through their feet.

I’m not making this up!

It can apparently be difficult to drive stock into a building across the PD that could be created by an unbonded floor. This could be a long-forgotten reason why livestock buildings are selected for special treatment in guidance notes.

Farmers have apparently blamed supernatural influences at work, when the real reason was a volt or two between a building’s floor and the ground outside

Otherwise what’s so special about ‘livestock’ buildings? Don’t forget that most houses are occupied by primates.


You're correct in what you say regarding the PD but what is special about livestock is the distance between front and hind legs, that makes a massive difference in PD difference susceptibility.
 
Well for a relative novice like myself it's hard to know where to draw the line.

This quote is from another thread:

In that case you may have a problem using your PME earth in this building, especially if your kids are going to be playing with hoses bare footed. There could well be a potential difference between true earth and the PME earth in this instance. If you did have a grid in the foundation floor that could be bonded, then that would have been acceptable. Looks like your going to have to go the TT route.

http://www.electriciansforums.net/e...lding-design-considerations-2.html#post443510

So is it fair to say that any building with a concrete floor that might become wet and have people with bare feet standing on it should not be PME'd?
Or perhaps the length of the distribution cable will effect the decision.
Where do you draw the line?
 
Last edited:
Where farm animals and people running round with bare feet it can be/maybe a problem, otherwise no problem!! If re-bar mesh, or grid incorporated in the the concrete floor foundations, even better ...lol!!!
 
What another cracking thread. So in summary so I can go forward,

1) We can export if practicable, if not TT it with all the usual requirements.

2)If we do export then a 10mm Main bonding cable must be provided, if services enter the location

3) If the CSA of the supply cable is <10mm we must provide a separate Main bonding conductor of 10mm

4)If the supply cable CPC CSA is > 10mm or + we can use said CPC as our 10mm main bond

Have I missed anything ?
 
Have I missed anything ?

A look at GN8 suggests you may need a bigger CSA than 10mm, if the earthing conductor serves a dual purpose ie. as a CPC and main bonding conductor as it has to be large enough to cover the worst case scenario for both, this is why it is suggested to run a seperate 10mm for the bonding.

Edit: when using the armour as the CPC combined with a core also as a CPC, the combined CSA often covers the most onerous conditions.
 
Must admit I fell for the contact DNO one a minute ago.
I've never understood where this 'can't export PME' stuff has come from, it's all pretty straightforward if you know your stuff.
If exporting the earth bond back to the MET, if not TT and use your MET in the DB board.
I know there can be more to it, but that's the basis.

you can export on a TNS SYSTEM IF TNCS TT ONLY OPTION
 

Reply to A good guide For 'exported PME' and outbuildings! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
923

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top