do they really,? none that I have seen actually do, they simply combine the N E at the head and I dont ever see the street getting dug up to rod the joints.
you are still getting confused and making out that TNCS and PME are the same thing, they are NOT
BS 7671 doesnt ask for 200 ohm Ra , so thats yet another myth you are perpetrating, and to simply bang in a single rod and rely on RCD protection, well thats the forte of all these so-called 'all the kit, full of it' done my time in 5 weeks sort of sparks that have destroyed a proper trade we used to have.
you obviously dont understand earthing by a few of the points I just mentioned, 200 ohm for a TT system, where did you actually pick that number from?
yes, after seeing quite a few installs with either broken neutrals or reversed polarity from localised transformers I dont like TNCS,
because they actually have proper PME systems, unlike the UK which has a poorly planned TNCS system which they are now trying to claim is actually PME to comply with their statutory obligations that come into force next year.
I think we've had this argument before haven't we?? And we both know you don't like TNC-S!! ...lol!!
So you've never seen a DNO's PME'd joint , i thought not!! As i stated to you before TNC-S distribution is a PME system in progress, the suppliers will NOT purposely leave you with a permanent unsafe earth connection, regardless of what you may think, full stop!! It may well be, that a local TX system network under progress of being converted to PME, will have a higher value of Ze than 0.35 ohm But it will never be higher than the TN-S system it's replacing. I can't remember the actual max they allow in those circumstances, but certainly a good deal lower than 0.60 ohms... The figure will depend on the TX neutral bonding, lengths of the strings, the ground types and the amount of joints already converted. I also think that a earth electrode should always be included at a PME service head, as part of that conversion...
I don't know where you live, but where i came from, if a head was converted to a PME connection, only the bonding and CU earthing conductors were left in place, pretty dammed pointless connecting a failed or failing sheath that stops at the head!!! Far more prudent to insulate any short lengths of bared, exposed lead sheath... Though i have no problem with bonding it where necessary, as an extraneous source of earth.
They do ''NOT'' as you are suggesting, just use the failing or failed sheath of a supply cable as the means of earthing the neutral, that's just a pure nonsense!!
BS7671 uses 200 ohms as it's max Ra. (it's not a figure i just pulled out of the hat) So even the most experienced electrician can walk away from a TT system they have just created with that value Ra. So, though i will agree with you on the 5 week wonder apprenticeships, and to the demise of our industry that we once had, there are still plenty of old hands that take notice of that BS7671 200 ohm Ra, and think it's a good-un!!
I think i understand earthing systems (especially TT systems) far better than you obviously do, of all types and of all descriptions. I've also probably been responsible for putting more rods in the ground than the membership of this forum combined, or very close to it!! And anyone that would diss a domestic TN-S system, for a 50 ohm Ra TT system and an RCD, ...is clearly daft, and i would argue, that He certainly doesn't understand what he's doing!!!
I don't believe a word of your witnessing several full broken neutrals, if you see just one, you would be doing well!! Got any documented facts about all these broken network distribution neutrals, that happen according to you on a regular basis, have you?? Reversed polarity is another matter altogether!!
Haha!! I've heard that little gem before, about Europeans using ''proper'' PME systems!! I think you need to cross the channel and see for yourself some of the standards of there local distribution companies, then come back and tell us about it!! lol!!!
The DNO's can't claim anything, that doesn't comply with ''Statutory Regulations and obligations''!! They have an obligation when so supplied/provided, to maintain a working and safe earthing point that meets those regulations. Extending a PME zone of protection is by far, safer than isolating it, then banging a rod in the ground!! And that's not a Myth!! Nothing stopping you including a rod at the extended location either, if you so wished!!!
Seems quite ironic really, in one hand you state European countries have proper PME, and in the other, the fact that most of the DNO's in UK these days, are owned by the very same European companies that operate these distribution systems in these countries!!! And probably with more statute regulations to adhere too, than they have in those European countries!!
I have no time whatsoever for myths and scaremongers!! And if you are who i think you are, ...you are one of the biggest scaremongers out there. Keep your scaremongering to the other forum, where many actually believe what your telling them. Here we have no time for your (or anyone else's) blatant scaremongery, based purely on what you like and don't like and myths, they are just your own biases....