A rant about a Chris Kitcher book
I bought this book over a year and half ago to do 2382/2392. Back then I noticed a few small things that were not right. Especially when cross referencing them with the GN3 etc. Afer doing some of the exercises in the back of the Chris Kitcher book on Inspection and testing second edition it appears that some of the basic principles for calculating R1 + R2 are not correct. In particular it is the books lack of ability to divise the r1 + r2/4 to get an approximation of R1 + R2 calculated from the m/ohm/m value and the length of the circuit given to you in the exercise. All of the answers lack the division. It's either me or I'm going banana's. But I feel let down by this book that I've paid hard earned money for lol something that if I didn't have any other book I would be calculating the incorrect answers...does anyone agree with me, has anyone seen this as well.
Rather than ranting about it on here why don't you get on to the publishers of it? They should pass your concerns on to the author who should respond to explain himself.
Hi rustynails,
I've recently bought this book, latest edition as far as I know (2013?). Can you post up the question number, and/or a few words from the question or answer? I will check when I get home. :)
To be fair this has been brought up a few times with regards to mistakes made in the book.
However once you are well into your studies the mistakes should be easy to identify and give you confidence that you are taking in what you have learnt!
As you have said GN3 is the main reference re the exam along with BS 7671 !
I take it that the book concerned is the practical guide to inspection ,testing and certification ?
Good luck with your studies
it has ( or had) a few mistakes but all in all, it's a good book. have you watched some of his videos on youtube? quite educational and he does well with the explanation of what he's doing.
Agreed :)
GN3 is not without its own errors:
This is meant to represent an IR test of a single final circuit (as opposed to an IR test of the complete installation, which is shown correctly in the previous figure).
Agreed :)
May be my eyes aint that good could clarify your point please Oh I get it circuit breakers on right?
What specifically (as in page number, etc) is wrong...?
To be honest if there is a problem with R1+R2 it'd have passed me by anyway, I didn't learn it from that book.
The grammar at least is spot on in that book.
well for example in the q & a at the back page question 26:
A lighting circuit is to be wired in 1mm twin and earth cable, the circuit is protected by a 5A BS 3036 fuse. What would be the maximum length of cable permissible to comply with the earth fault loop impedance requirements (Zs)? (Ze is 0.45)
Answer:
From table 41.2 Zs for a 5A BS 3036 fuse is 9.58 ohm.
The R1+R2 value for 1mm copper from Table 9A is 36.2mohm
Maximum resistance permissible for the cable
18.5 - 0.45 = 18.05
Maximum length of circuit is:
18.05 x 1000 /36.2 = 498M
Where does the 18.5 figure come from?
rustynails,
GB.Kayak,