bit stuck on this job got a consumer unit (in a barn) fed from a house (tns) 3 phase mcb 63 amp the zs at the barn is 0.76 but after adding a rod and making it TT managed to get zs down to 0.5. ive got to add fire alarm panel and another sub board. there will be 100ma rcd before the consumer unit but the bit im stuck at is should the fire alarm feed also be before the 100ma rcd and what about the sub sub board, its 25m away from the sub board in 16 mm armoured.... would the best thing to do to add 300ma main rcd off that add 100ma to both the sub boards then 30 ma from there ? any advice appreciated

just to be clear it goes like this..... house tns with main board> barn sub board fed from house (also fire alarm going in same place ) > sub sub board fed from sub board
 
Couple of questions.
What is the purpose of this outbuilding isit a leisure building, why does it need a fire alarm?
Are there any extraneous conductive parts?
What size/core swa is feeding the outbuilding?



going to be a shop
no extraneous conductive parts all plastic
its all 16mm but upgrading will be as bad as getting a new main in. so customer said no to upgrade
 
why are you trying to make it to a TT system in the barn when their is no extraneous parts in the barn?
because customer doesnt want rcd in the house so i was going to make the barn tt but while im typing this just realised my mistake, board in the house would still need rcd for fault protection. how do i get a fire alarm in the barn and get sufficient fault protection on a 63 amp breaker in the house. can i put 300ma rcd in the house after the main board then put the fire alarm on before the sub board and before 100ma rcd or can the fire alarm not go on any rcd whatsoever ?
 
I think the gyst of the thread is that the Zdb in the barn is too high for the 63a MCB although I don't have a BYB to check it. If that's the case I'd be looking to change the OCPD to a type which meets the disconnection time rather than adding RCD's where they are not otherwise required
i would need to take it to 45 amp and wouldnt be sufficient for the shop
 

Reply to Adding sub board to main consumer unit on tt in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
854
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top