blackpool
bit stuck on this job got a consumer unit (in a barn) fed from a house (tns) 3 phase mcb 63 amp the zs at the barn is 0.76 but after adding a rod and making it TT managed to get zs down to 0.5. ive got to add fire alarm panel and another sub board. there will be 100ma rcd before the consumer unit but the bit im stuck at is should the fire alarm feed also be before the 100ma rcd and what about the sub sub board, its 25m away from the sub board in 16 mm armoured.... would the best thing to do to add 300ma main rcd off that add 100ma to both the sub boards then 30 ma from there ? any advice appreciated
just to be clear it goes like this..... house tns with main board> barn sub board fed from house (also fire alarm going in same place ) > sub sub board fed from sub board
Sounds if you pulled a 16mm cpc in with the sub then this would get you too your max zs value. Is this doable? Stay away from rcds & mcbs on large subs if possible for discrimination of ocpd in series during fault condition. Even if you end up TT the barn the sub would still need to meet TN disconnection times up to the isolator. Understand your in a pickle but dont get led by the customers "tight budge" as you will still need to cert your work.
It's a 16mm 4 core armoured. Not much volt drop at all. It's about 30 meters but that's just from r1 and rn test and rough distance
Not much at all? That's a great answer to a technical question.
A quick smoke packet calculation based on the full ratings of the ocpds suggests that your looking at 4.5V drop on the 63A submain and 3V drop on the 50A submain after that, giving a total of 7.5V drop on the submains alone.
That leaves you very little left for your final power circuits and nothing at all for any final lighting circuits.
Reply to Adding sub board to main consumer unit on tt in the UK Electrical Forum area at ElectriciansForums.net
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...