When installing a 'garage cu' adjacent to the main ccu to accomadate an RCD for connecting a TL inverter, what cable size would you use to link the cu's , less than 400mm run
 
When installing a 'garage cu' adjacent to the main ccu to accomadate an RCD for connecting a TL inverter, what cable size would you use to link the cu's , less than 400mm run
How & where you intend connecting to the existing install will govern what size cable you will need to use i.e what rating is the overcurrent protection at the point you are connecting to....is it the suppliers fuse or an MCB etc??j
 
I was thinking of replacing the Henley block for an isolator, and wondered if I could feed it in there and bypass the CCU, using the same size tails (25mm/100A incomer)
 
What size KWp is this system. As it is domestic I assume you are staying within the 4kw range of things then 16amp protection is all that is needed.

So is there a spare way on the existing CU, if there is use that as it will be cheaper for you client. Take a supply from the spare way to the new enclosure, protected by a 16amp MCB. Fit a Double Pole RCD, as you said on a previous post it is transformless type Invertor so you need a B type RCD.

If there is not a spare way, why do you want to remove the Henley Block ? Why do you want to feed the enclosure that is going to be maximum 16amp with 25mm tails? Are you planning feeding both the existing CU and the enclosure via this isolator you intend to fit?
 
it a 2.6KWp system. We are doing a ccu change, so was going to put in an isolator switch, its an SMA inverter which according to its specs says a type A RCD, from reading the DTI guide I got the impression that a, you have to oversize the cabling, b) you must keep the ac supply seperate from any other circuits
 
it a 2.6KWp system. We are doing a ccu change, so was going to put in an isolator switch, its an SMA inverter which according to its specs says a type A RCD, from reading the DTI guide I got the impression that a, you have to oversize the cabling, b) you must keep the ac supply seperate from any other circuits

So you now going to change the CU completely, and still fit the garage type CU?. So again are you going to fit the one isolator for both CU and garage type CU ? or are you going to fit Isolator then a set of Henley's and feed the 2 points from there.

Again yes agree if you wished to fit 25mm tails to the main CU, but you may not need 25mm tails to the Garage CU have a look at Reg 434.2.1

point 1 then if the manufacturer instructions say A type is fine then good. Point 2 ...............hmmmmmm had this before.
 
the design is thus- From the meter 25mm tails to iso switch then 25mm to henly, 25mm from henly to CCU, and 25mm from henly to RCD in seperate enclosure+ lockable ac isolater etc,
the proposed 25mm cable in total will not be greater than 2 metres
 
You can probably miss out the henley; just take both cables from the output of the isolator. The second cable only needs to be 4mm/6mm which is likely to fit in the terminals with a 25mm. It is protected from fault by the DNO fuse (unless the DNO has specified a minimum cross sect area).

The SMA installation instructions do NOT require a rcd. They say if an rcd is required then it must be a minimum of 100mA. And type a rcd is fine for SMA TLs.

Also, as there is only the one device on the circuit, the inverter, then there is no need to protect against overload from the mains side of it, only fault.

Regards
Bruce
 
You can probably miss out the henley; just take both cables from the output of the isolator. The second cable only needs to be 4mm/6mm which is likely to fit in the terminals with a 25mm. It is protected from fault by the DNO fuse (unless the DNO has specified a minimum cross sect area).

The SMA installation instructions do NOT require a rcd. They say if an rcd is required then it must be a minimum of 100mA. And type a rcd is fine for SMA TLs.

Also, as there is only the one device on the circuit, the inverter, then there is no need to protect against overload from the mains side of it, only fault.

Regards
Bruce[/QUOTE
 
Last edited:
If you don't fit an RCD B type as fault protection then you have to install an Inverter that will not allow DC fault currents back into the AC side.

So the use of simple separation by a transformer was the way round that.

If the SMA Inverters are transformerless, and do not need a Type B RCD protection, then they must have either another form of separation, or the capability of not to allowing those DC fault currents to pass through.
 

Reply to additional cu cable size in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar threads

Sounds more positive.
Replies
8
Views
551
dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
502

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top