Yes but seemingly no according to the DTI.
I can only relate to normal electrical practices and if you were in a domestic installation and taking a sub main out to an out building, if that building have metallic parts to it either a metal service such as a water pipe, or the construction of the building was metal, then you would need to bond the extraneous conductive part back to the MET if you were exporting the PME earth. If you were not exporting the earth perhaps because the building was a long distance from the origin of the supply, then most likely you would TT system.
There is obviously a reason the German electrical industry do not export earths on a PME, to which I don't know, and so it seems they insist on the array being bonded via a separate rod. I have no problems with this as such, as long as you are not having other metal work at a different potential that can be touched while your working or touch the array frame, and I used the example of perhaps an aerial mast that is earthed via a PME/TN-S from within the equipotential zone.