Thankyou. Can you help me with my calcs? Am I able to apply a 0.4 disconnection time to a supply circuit?Yes it applies but you need to alter the 'k' factor for aluminium
Fault current is 800AThankyou. Can you help me with my calcs? Am I able to apply a 0.4 disconnection time to a supply circuit?
Sorry it's a building with a block of flats the flats are fed from meters located in a communal hall with each flat fed from the bemco, I've never really understood why a shorter disconnection time requires a smaller earthing conductor, as It stands with a 5 second disconnection time min earth would be 18mm but with 0.4 disconnection time it drops to 5mmwhat do you call a supply circuit? if it's a distribution circuit, 5 secs. max. applies, but the time/current graphs will give you the actual diss. time .
Those graphs make my eyes goes fuzzy ?yeah, but those figures are the max. allowable diss. time, not the actual time which you get from the time/current graphs.
so you need to look at them again and again... works with beer. eyes fuzzy after a few.Those graphs make my eyes goes fuzzy ?
Ok so 60A semi enclosed fuse at 800A gives me a dis time of 0.2so you need to look at them again and again... works with beer. eyes fuzzy after a few.
Because the fault clears quicker and the conductor will not get to a high enough temperature to melt, if it was 5 seconds there's plenty of cooking time.Sorry it's a building with a block of flats the flats are fed from meters located in a communal hall with each flat fed from the bemco, I've never really understood why a shorter disconnection time requires a smaller earthing conductor, as It stands with a 5 second disconnection time min earth would be 18mm but with 0.4 disconnection time it drops to 5mm
I will have to check but the min size is 10mmsqDoes anyone know if the adiabatic equation applies to aluminium conductors when calculating the csa of earthing conductors, or guide me to where I might be able to find an answer.
Cheers
Did you check?I will have to check but the min size is 10mmsq