Considering that fault currents can be in the thousands of amps it will probably take a fraction of a second for the eddy currents to become a problem. Don't forget current has more effects than just heating the conductor, the magnetic fields will cause mechanical stress at those levels.
Have to take your word for that Dave, it's a science that I know nothing.
I did a job a couple of weeks back where the lives to a three phase board were all taken into the board through their own neatly drilled 20mm hole. At the time each phase was drawing about 20a, there was no heat or sign of any damage. It had been like this for 20 years.
Thought I would invest in the latest copy of Guidance note 1, Selection & Erection. Curious, I looked up 'Ferromagnetic enclosures, cable entering; (521.5.1) All the conductors of a circuit should generally follow the same route. Live cables of the same circuit may cause overheating if they enter a ferromagnetic enclosure through different openings (page 97, 7.4)
exactly what i was getting at, the earth is only live during fault conditions
That isn't true. There will be a certain amount of legitimate earth leakage from appliances. Don't forget that there is functional earthing as well as protective earthing.
And as pointed out, under fault conditions there could be a significant current flowing.
Also there will be some voltage and current on the earth conductor where PME conditions apply.
When the SWA is used as the CPC outside the box, and a length of 6491X lugged onto the banjo bolt serves on the inside, the low resistance path connecting them together is via the brass of the banjo and the bolt, rather than through the enamelled steel enclosure which might make relatively poor contact and is of lower conductivity compared to the brass. So in the event of a fault the banjo bolt carries most of the fault current through a separate hole.
What's the solution? Single hole banjo? Moebius bolt that goes through both holes and back to where it came from? Slot the banjo bolt hole across to the gland entry? :)
Do like I do and put the banjo inside?
Not an issue really outside or inside, the contact area is greater inside, than out.
Don't drill the enclosure, why would you?
There is no functional earthing in a domestic installation.
Indeed, functional earthing is where most legitimate leakage current comes from. Not that it has anything much to do with eddy currents - they start being a problem with hundreds of amps, not a few mA.
Advice on regulation 521.5.1
Thread Tags
spadge47,
HappyHippyDad,
TrueNAS JBOD Storage Server