Wrong.
Correct.
Wrong.
Right.
It's like a ping pong ball!

Wrong.
Correct.
Wrong.
Right.
Wrong.
Why spin?Did they not introduce a new Regulation in the 17th allowing a separate earth to be run along side an SWA cable?
Obviously the earth would have to enter the enclosure separately to the other conductors.
Why spin?
it has always been acceptable, whilst ill advised to run a "separate" earth (cpc) alongside an SWA, as both the SWA & the "earth" must be capable of carrying they full fault current and suitably terminated to meet the requirements, so it is just a waste of money to do this.
So nothing has changed.
It is still stupid to waste money on a separate cpc, so why bother?
They don't allow it to enter through a different point, never have.Can someone please explain why the Regulations allow a separate earth with SWA to enter ferrous magnetic enclosures, but not when the conductors are not part of an SWA cable?
Can someone please explain why the Regulations allow a separate earth with SWA to enter ferrous magnetic enclosures, but not when the conductors are not part of an SWA cable?
They don't then can you explain how it is possible to correctly terminate an SWA cable, and slip in the separate earth cable?They don't allow it to enter through a different point, never have.
dave,The only reason I know of to run a seperate earth is when if is required to meet bonding requirements rather than as a cpc
They don't allow it to enter through a different point, never have.
They don't allow it to enter through a different point, never have.