davesparks
dave,
I never mentioned bonding conductor, only referencing a cpc as an "earth" using the term "earth" as it had been used in an earlier post.
A bonding conductor is not part of the circuit that the SWA is supplying.
How exactly does one inform that bonding conductor that it is not to be a cpc? Regardless of what it gets called it will still be a part of the earth loop and carry it's share of the fault current.