OP
spadge47
I presume main protective bonding conductors are also appropriate protective conductors and therefore they need to enter through the same hole as the main tails if they all had to enter the same.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Advice on regulation 521.5.1 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
They don't allow it to enter through a different point, never have.
Not according to the copy I have here.
Yes, as I said, read and UNDERSTAND the reg.
Where it is REQUIRED.
If it is not REQUIRED then it is NOT ALLOWED.
So, if you can generate a scenario where it is REQUIRED, then it is ALLOWED.
However, I doubt you can actually prove a reason to install a separate cpc.
Look it up do the calcs, and then come back and show where a seperate cpc is REQUIRED, considering that the SWA must act as an adequate CPC for the circuit anyway else it is not acceptable.
In which case as the fault current WILL be split equally then it is a requirement that the armour WILL take the full fault current, thus the additional wire is not required.
The fault current will NOT split proportionally between the two conductors, at least not according to the research undertaken by the independent body that is the ERA.
Thus the SWA & the additional "cpc" must be capable of carrying the full fault current, thus, there is no need for the additional cpc.
QED.
states within the same enclosure not entry point so whats wrong.
L+N dont need to go through together if you slot it, or use paxolin/similar
you dont need to slot it for the cpc though, eddies wont affect it and if it does you have bigger problems.It also states they must only be surrounded collectively by ferromagnetic material where they enter.
If it is slotted or paxolin is used then it is still a single hole in the steel!
you dont need to slot it for the cpc though
enclosure is not the same as entry hole, take that how you will.Yes you do, which is the point that has been made here, and it does state it quite clearly in that regulation and I, along with others, have been corrected on in the usual helpful manner from a certain ****
Wrong, read 521.5.1
Send your copy back & get a genuine one.
You're now saying it is allowed I think.
enclosure is not the same as entry hole, take that how you will
enclosure is not the same as entry hole, take that how you will.
the reg
"the conductors of an ac circuit installed in a ferrous enclosure shall be arranged so that all line conductors and the neurral conductor, if any and the appropriate protective conductor are contained within the same enclosure"
Not according to the theory and research done by ERA, now if you know better then ERA then good on you WTF are you doing posting on an internet forum?It will split proportionally, it will not split equally. I've read differing information on exactly what those proportions will be, with a general consensus that the majority of the fault current will flow through the armour.
I am not talking about an additional cpc, I am talking about a bond run in parallel with the armour (as cpc), this is still a protective conductor
It also states they must only be surrounded collectively by ferromagnetic material where they enter.
If it is slotted or paxolin is used then it is still a single hole in the steel!
Firstly 521.5.1 is EXACTLY what I have been referring to, it states REQUIRED.
If it's not REQUIRED then it's NOT ALLOWED.
I have said this from the start.
You NEED to understand when it is REQUIRED, by BS7671, not just a whim.
If it's not required, then it's not allowed, so, when is it required?
Almost never if ever.
Next.
I can't send my copy back as I don't have a paper one the IET host it for me, so I am told by them that I always have the latest version, and my comments above relate to that.
So, if you check the current version of BS7671 (i.e. Amd 3), you will see that my comments relate directly to that and are not contradictory in any way.
IF you can find a reason where by a CPC has to be added to an SWA then it's fine, but, that must be by calculation just coz you want to does not count as a regulation in BS7671.
Now, IF the calculations require an additional cpc, then it is doubtful that in most cases the SWA is adequate.
I am NOT saying it's allowed, UNLESS it is REQUIRED, if you can prove it's REQUIRED then it's allowed, how often is it REQUIRED under BS7671, I would go for about 1% of installs.
enclosure is not the same as entry hole, take that how you will.
the reg
"the conductors of an ac circuit installed in a ferrous enclosure shall be arranged so that all line conductors and the neurral conductor, if any and the appropriate protective conductor are contained within the same enclosure"
Reply to Advice on regulation 521.5.1 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net