I cant see how to collectively take main tails and earth all in one though, because the main bonding (water/gas) must have to go through the same holes as the tails
 
The regulation says protective conductor, not circuit protective conductor

We are discussing circuit protective conductors.
This is where this started, and it has not changed, as I have said from the start, where it is REQUIRED.
Now you are trying to change the topic to something else to try to make it look like you were right when you were wrong.

Look the devil is in the detail, the word is REQUIRED, it it's not REQUIRED, then it has to be collectively surrounded by ferrous material.
IF it is required, then it is almost definitely not a cpc, thus not part of the original discussion, end of.
 
I cant see how to collectively take main tails and earth all in one though, because the main bonding (water/gas) must have to go through the same holes as the tails

No because they are not part of the supply circuit supplying the power to the board.
They are BONDING conductors not cpc's.
 
We are discussing circuit protective conductors.
This is where this started, and it has not changed, as I have said from the start, where it is REQUIRED.
Now you are trying to change the topic to something else to try to make it look like you were right when you were wrong.

Look the devil is in the detail, the word is REQUIRED, it it's not REQUIRED, then it has to be collectively surrounded by ferrous material.
IF it is required, then it is almost definitely not a cpc, thus not part of the original discussion, end of.

The discussion started with an earthing conductor, which is a protective conductor which performs the functions of both cpc and main bond. I was wrong about the question, now despite your unhelpful attitude I have learned that I was wrong and think I can see why the regulation is the way it is.
 
imagepng
 
Read and understand the relevant reg.
IF the 3 conductors are part of the same circuit then they must be collectively surrounded by ferrous material, unless they come under the deviation in the 3rd paragraph.
Someone has posted a pic of the book earlier, look at it, read it and understand it, then all will become clear.
 
The discussion started with an earthing conductor, which is a protective conductor which performs the functions of both cpc and main bond. I was wrong about the question, now despite your unhelpful attitude I have learned that I was wrong and think I can see why the regulation is the way it is.

Where did that come from?
Now you have me confused!
 
We are discussing circuit protective conductors.
This is where this started, and it has not changed, as I have said from the start, where it is REQUIRED.

No Paul, this is your post No 24

They don't allow it to enter through a different point, never have.

You slipped the 'required' red herring in later, I assume when you actually read 521.5.1

Why do you keep repeating the word 'required' it's irrelevant. You either can or you can't bring the protective conductor through a separate opening.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on regulation 521.5.1
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
156

Thread Tags

Advert

Thread statistics

Created
spadge47,
Last reply from
HappyHippyDad,
Replies
156
Views
37,318

Advert

TrueNAS JBOD Storage Server

Back
Top