Hi.

Been reading the but around 427.1.7.

Does anyone have any idea on retrospective application?

Is this going to apply to every board change or just adapted to new builds and then as a C3 recommendation for everything else?

Given prices it's going to be a massive cost change on a board swop. Plus, I know for certain I'm going to have space issues with anything over 30 years old here in Fife.

Thoughts?
 
Until the make a single module arc fault breaker that can retro fit most boards and costs less than £50 a pop then they are a non starter imo
 
Regulation 421.1.7 has been redrafted. It is now a requirement (rather than a recommendation) to protect final circuits supplying socket-outlets and fixed current-using equipment with a rated current not exceeding 32 A by arc fault detection devices (AFDDs).

So the majority of circuits basically?

I've never looked at AFDDs before.

Do they have built in overload and RCD protection or are they an additional device?

Are they one device per consumer unit or one per circuit?
 
Regulation 421.1.7 has been redrafted. It is now a requirement (rather than a recommendation) to protect final circuits supplying socket-outlets and fixed current-using equipment with a rated current not exceeding 32 A by arc fault detection devices (AFDDs).

So the majority of circuits basically?

I've never looked at AFDDs before.

Do they have built in overload and RCD protection or are they an additional device?

Are they one device per consumer unit or one per circuit?

Those that I've seen (Crabtree & Wylex) are single module RCBOs, with AFDD incorporated.
 
Regulation 421.1.7 has been redrafted. It is now a requirement (rather than a recommendation) to protect final circuits supplying socket-outlets and fixed current-using equipment with a rated current not exceeding 32 A by arc fault detection devices (AFDDs).

So the majority of circuits basically?

I've never looked at AFDDs before.

Do they have built in overload and RCD protection or are they an additional device?

Are they one device per consumer unit or one per circuit?
MCB/RCD/AFDD combination, one per circuit, like a RCBO on steroids
 
MCB/RCD/AFDD combination, one per circuit, like a RCBO on steroids
And a price tag to match:
For comparison, the Wylex RCBOs:
 
Nobody will get board changes done when the board costs £2k on its own when they can get a BG from screwfix for £70, it's bad enough now! completely counter intuitive regulation
I see the "what price do you put on safety" comments now but I think making them mandatory is a step to far IMO especially when the AFCI's used across the pond don't appear to get good reviews as to how beneficial they really are.

I see a lot of problems on the horizon when these combined units start tripping is it an overload, is it an earth fault or is it an arc fault or is it a faulty protection device, ok it is easy to eliminate any overload but there are still 2 components within the protection device that need to be verified ok the RCD function can be tested but that leaves the AFDD function so do you swap the device or do you rewire the circuit or both, yes we are told the AFDD has it's in built function test but so does an RCD and that push button test does fail occassionally

I really feel the industry hasn't had the time or taken the time to properly evaluate the AFDD and inform and educate the trade of the pro's and con's before forcing the fitment of them. How long was the ELCB / RCD around before fitting them became the norm and was then more or less mandated

I think the AFDD is going to be a hard sell looking at the links in a previous post a 550 - 600% increase in cost for the protection devices alone is no doubt going to increase the posts on here by some customers who think the electrician who has told them they need a new CU at a cost of a few thousand pounds is ripping them off
 
So is there no AFDD which can be installed and protect multiple circuits (like an RCD on a dual split board for instance)?
An AFDD that covers more than 1 circuit would be a nightmare.
 

Reply to Amendment 2 and AFDD's in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
430
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
    • Like
2
Replies
15
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top