Dave Appleby

-
Arms
Joined
Mar 19, 2018
Messages
163
Reaction score
207
Location
Scotland
Hi.

Been reading the but around 427.1.7.

Does anyone have any idea on retrospective application?

Is this going to apply to every board change or just adapted to new builds and then as a C3 recommendation for everything else?

Given prices it's going to be a massive cost change on a board swop. Plus, I know for certain I'm going to have space issues with anything over 30 years old here in Fife.

Thoughts?
 
isn't that the sdame for an afci?
Not quite.

An RCD will detect a "parallel arc" between L & E, as well as simple leakage due to non-arcing conduction. But it won't detect a fault between L & N (that is below the OCPD) nor a series arc where a small break in L or N has happened.

An AFDD should pick up the high frequency content of the arc and so trip on L-N faults and series arc faults. But other things also produce arc noise.
 
Not quite.

An RCD will detect a "parallel arc" between L & E, as well as simple leakage due to non-arcing conduction. But it won't detect a fault between L & N (that is below the OCPD) nor a series arc where a small break in L or N has happened.

An AFDD should pick up the high frequency content of the arc and so trip on L-N faults and series arc faults. But other things also produce arc noise.
thx PC
i had thought the main component was the same, a toroid .......at least to the extent of my reading......

as ro the 'frequency' and/or arc waveform, we're told our AFCI incorporates a microprocessor with special algorithm software

the details of which, we're not privy to, but the testing lab methods we are>>>

This is what they used....a 'simulator;'.....

https://i.Upload the image directly to the thread.com/eOF06wB.jpg
Do RCD's have this manner of testing?

~S~
 
The AFDD probably have a toroid as well, but it would need to be another in (probably) the L so it can detect the faults that a RCD is designed not to (L-N flow). By frequency I mean a typical earth faults sees a lot of 50Hz flow, but an arc typically has components to over 10kHz.

As far testing - that is a sore point. In the UK electricians typically have a Multi Function Tester (so high voltage IR, few 100mA bond resistance, supply Zs, RCD trip, voltage, and probably phase rotation, maybe earth rod impedance via two spikes, etc) but I have not seen much sign of them being available to test AFDD. We are being told to trust the self-test button, etc. Yes, what a good idea...
 
If they don't work on ring circuits and not required over 32amp and ineffective on lighting circuits afdds seem pointless.
I can see some cases for them, but the cost/benefit looks very poor to me.

They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.

But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.
 
I can see some cases for them, but the cost/benefit looks very poor to me.

They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.

But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.
I agree, I know alot of electrical fires are due to faulty white goods, there has been talk that it is in fact the white goods industry are pushing for us to incorporate AFDD to protect plugged in equipment.
It all seems like a box ticking exercise to me, there's no data I'm aware of.
 
I agree, I know alot of electrical fires are due to faulty white goods, there has been talk that it is in fact the white goods industry are pushing for us to incorporate AFDD to protect plugged in equipment.
It all seems like a box ticking exercise to me, there's no data I'm aware of.
Maybe we should be pushing for the white goods industry to stop throwing cheaper & cheaper components into their appliances then we wouldn't have this problem!
 
I can see some cases for them, but the cost/benefit looks very poor to me.

They do work on RFC but don't detect an open ring as practically no arcing takes place there as voltage difference is very small, however, they should detect arc faults on appliance cables that are attached that are above the few amps threshold.

But again, where is the evidence for their use? That is a proper analysis of fire (or near fire fault) cases that clearly would have been stopped by an AFDD and not things like lint fires in tumble dryers, etc.


Funny you mention evidence. In the US, other than cut wire wrapped in glass tape and hooked up to a neon gas transformer in a laboratory there is zero evidence that arcing is behind any residential fires to begin with.

There is the case of firefighters opening walls to find smoldering studs with romex stapled across them. However, pyrophoric carbonization from an energized staple likely to be the real cause behind these events was and is miss-theorized into arcing. Ignoring the evidence of dried wood around nails and the foundation some distance from the smoldering area indicative of low level current leakage over the years and not arcing.
 

Reply to Amendment 2 and AFDD's in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
    • Like
2
Replies
15
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top