S

super

hi all thanks for any advice,i am looking into installing a contactor to switch multiple lighting circuits i cant find a design current supply needed to switch the contactor in any documents apart from mA ratings, the norm i always see is 6amps which is what i plan to use at the consumer unit to supply the contactor but why is it always taken as 6amps im sure looking at this contactor it requires mA but do we use 6amp mcbs as these are the smallest in general stock? are contactors designed to take a 6 amp supply to switch them over? im having to do a circuit design for the contactor and looking to start with the Ib rating and failed straight away,so only now asking the question after years of installing a 6amp mcb any knowledge very welcome thanks
 
A control circuit could be in place for a single switch to operate a single contactor, or multiple relays and switches and other input devices to operate multiple contactors.
The control MCB should be selected accordingly.

Most of the Industrial / commercial control circuits I've worked on generally have a 2 or 4 amp control MCB or fuse.
 

Reply to another contactor question sorry in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
670
  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top